Thank you very much,
as i am freshly looking into the manual of my GX device under point 11 i see that my chosen option is lead acid, since that is closest to agm in my case, and in 11.2 it states agm in the list also 
And in that colum it states that svs, sts and scs all should be enabled
So i did that, except the sts since i don’t have a tempsensor for my batteries
To my understanding the BMV712smart is the chosen instrument to measure voltage and amps, as i set it up this way in my GX device
The readout of voltage according to bmv, cerbo, chargecontollers and my multimeter all seems to high 60.1 volt for instance while in absorption and suposed to be 58.8volts.
Setting the svs on or of and rebooting the system does not seem to influence it, also the limit charge voltage does not influence it, but as you explained before, the voltage limiter only works on batteries with a bms, so thats ok.
My bmv is measuring directly from the poles of the batteriebank, so its accurate, and displays correctly a to high voltage
I do understand a voltage drop occurs in the cables, but on my system it is very small, since the cables are short and of adequate size and krimps etc. Are good, also with measurements with a voltmeter it is very satisfying and way below the 1.1-1.3 volts that somehow gets added.
Side note: "old"150/100 chargecontroller only has ve direct port that we used on Cerbo GX and “new” 250/100 chargecontroller has ve can port that we used. As shown in 11.2 i checked my firmware and all is in order
In 11.3 i also see that the internal charge algorithm is disabled and controlled by the charge voltage setpoint of the inverter charger,
Is this perhaps a possible problem?
Sidenote, since we are off grid, my charger in the inverter/charger is disabled.
I believe ess does not apply to us?
11.4 indicates also for all batteries, this includes agm, and these functions are discribed to should work:
-11.4.1 limit charge current
-11.4.2 limit managed battery charge voltage
(Side note, this does not seem to work, even after rebooting)
-11.4.3 shared voltage sense
(Side note should work with both my chargecontollers and it will use BMV for sensing voltage)(BMV indicates 60.1 volts while limit is set at 58.8V)?
-11.4.4 shared temp sense
(Side note we don’t have a temp sensor)
-11.4.5 shared current sense
(Side note: it is on and conditions are met)
-11.4.6 controlling bms
Not applicable i believe
I hope that this message gives you more insight of our system and how i set it up, ill go check the settings in my inverter/charger, to make sure thats not the problem.