Hi All I have a generator on ac1 in on Quattro 8kw. Plan to use grid if generator fails. I have a dse 3110, 0ne wire to start (close to start) connected to the no of relay 1 of the Cerbo. There is another wire to operate a stop solenoid for the fuel cut off lever. The dse holds this for 10 seconds. I have connected this to the nc terminal or relay 1. I cannot use any settings in the VRM as these are disabled when you select genset as the relay. In victron configure and thr generator start stop there is no separate option to stop the generator (it appears the stop is just opening powering down the relay) . Is there a way to do this with additional programmable assistants? Or do I have to somehow add in another external relay? Or some other solution? The dse it appears only requires a pulse in each case.
Hi Baz,
You should be able to do this with the Quattro Assistants. Given you’re working the grid and gen in reverse from normal, the premade Gen Assistant mightn’t quite suit. So build your own sequence of Assistants to do the whole job. You have a couple of output relays to play with and should be able to work something out.