So we need a 3 phase 400V 1.6A UPS for keeping a 3 Phase 400V 1.6A input, 24V 20A output power supply running in the event of a loss of power on an industrial machine. Can 3 x Phoenix Inverter 24/500’s be configured to run 3 phase?
Thanks!
So we need a 3 phase 400V 1.6A UPS for keeping a 3 Phase 400V 1.6A input, 24V 20A output power supply running in the event of a loss of power on an industrial machine. Can 3 x Phoenix Inverter 24/500’s be configured to run 3 phase?
Thanks!
No the Victron Phoenix Inverter 24/500 (500 VA model) cannot be configured for 3-phase operation. The small Phoenix 500 VA units are stand-alone inverters. They don’t support parallel or three-phase synchronization. Victron’s documentation is clear: only specific inverter/charger families such as MultiPlus, MultiPlus-II, Quattro, and larger Phoenix Smart Inverter models like the 1200 VA, 1600 VA, 2000 VA support parallel and 3-phase configurations.
The Phoenix 24/500 has no communication ports (VE.Bus) required for phase synchronization.