No, a 3 phased grid-tie-system needs a 3 phased AC-IN Connection.
Each unit requires a 120° angled ac-in supply to sync with during grid-parallel operation.
If one unit lacks its AC-Input, the whole system will disconnect from grid and run in offgrid-mode, doing its own microgrid.
Like mentioned before, you would need to create an off grid 3 phase system with a separate MP2 connected to grid (and USB MK3 adapter) to charge the batteries. So that means you need a total of 4 units of which 3 need to be the same model.
This isn’t very efficient as there won’t be any AC passthrough possible, so AC consumption on the 3-phase side always needs to be fed via the AC in on the separate MP2, which means you have AC → DC → AC conversion losses all the time.
If you have AC solar connected to the 3 phase system, that would work a bit better (DC Solar would be best)
This answers my question and probably saved me from buying two additional MultiPlus units for a configuration that would not work as expected.
I will proceed with the single-phase ESS and EV charger for now, and revisit the 3-phase option only if I upgrade to a 3-phase grid connection in the future.
That makes sense. My goal was to use a 3-phase Victron EV Charging Station while keeping my existing single-phase grid connection.
I understand now that this would require a separate MultiPlus for battery charging and three additional units for the 3-phase off-grid system, with continuous AC → DC → AC conversion losses.
In that case, it is probably not the most practical or efficient solution for my setup.
I will continue with my current single-phase ESS system and revisit the 3-phase option only if I upgrade to a 3-phase grid connection in the future.