I have 4 Renogy AGM 200 ah batteries inbound. Series parallel for 24 volt 400 ah. Renogy suggests installing a battery balancer. Victron is the hardware I use. I need help wiring it correctly.
Did you take a look at the manual?
There are a few examples.
You could also do it this way but balancing will be slower and less ideal as balance between packs is an issue. (One pack will be at a higher soc during charge and discharge first).
Your ‘bus bar’ in your set up are the terminals where you have your load/charge takeoff. You have to create a midpoint on both sets of 24v.
Appreciate the help , thank you
One more question, what guage jumper going from common to common in between series set would you suggest if I just used one balancer?
It only balances with 1A. So for the balancer it is not huge.
Wiring unlimited 3.5. Battery bank midpoint
I have never set up like you have, I am a fan of using bus bars.
There are other posts about it.