Hi all,
Small home setup. 100Ah AGM, 2 x 100W panels in serie, Smartsolar 75/15, Phoenix 12/500 and Venus on Pi.
Sofar I have never seen my battery indication as 100%. The MPPT nicely goes from Bulk via Absorb to Float and the battery is at 13.8
But in Venus or in Victronconnect I never see the 100% charge indication.
I always see “-”
Correct, no shunt.
Picked one of the presets (Gel Victron deep discharge(1) ) and checked the settings in the battery specs, which are ok.
Absorp: 14.30
Float: 13.80
Battery is 1 week old. Before I installed it, I fully charged it with a certified charger.
You refer to the charger settings. In the Inverter (you do not state which model) there is a setting under general which says “enable battery monitor” and you put in your battery bank capacity. Screen shot from one of the programming methods.
Unluckily your inverter does not include a battery monitor function so with AGM batteries you will not have any SOC readings. You could install a SmartShunt and connect that to the Pi with another VE Direct to USB cable.
The screenshot is from the PC programming app VE Configure for the larger, fully featured inverters.