Hi everyone,

Problem:

I have a moderately sized DESS system consisting of 4x 10k Quattros, with AC coupled PV. I’ve noticed when DESS schedules the system to idle (grid-to-loads), the idle DC consumption on the system is close to ~500W (which aligns with some others on this forum). This is obviously quite high so I’ve spent a while trying to avoid this.

Another observation was the system goes into a deeper idle when DESS is disabled and SOC at ‘ESS minimum SOC’ (consuming closer to 100-150W from the grid, with DC consumption close to zero). I believe this is because the inverter/charger circuit is turned off, due to peak shaving also being disabled (if configured as such).

—

Work-Around:

I set up a Node-RED automation that sets /Settings/CGwacs/MaxDischargePower to 0 (“Maximum Inverter Power” in Venus) when /DynamicEss/ReactiveStrategy is either 9 or 15 (the two seemingly relevant idle states). Otherwise it’s -1 (disabled).

I’ve verified this puts the system into the lower idle state, similar to as-if it were at ESS minimum SOC (it results in /Hub4/DisableFeedIn being set to 1)

—

Question:

I’m still testing but was hoping for the wisdom of the crowd — anyone see potential problems with this?

—

Add’l Background / Assumptions:

My utility offers a simple weekday on-peak (8 hour) / off-peak (16 hour) rate plan, and so most of the year my system is idling close to 12-14 hours during the night.. Selling back to the grid is not advantageous, but charging from the grid ahead of the peak hour can be.

  • When solar starts producing in the morning, I believe DESS will quickly change the ReactiveStrategy away from the two idle states above.
  • When DESS wants to self-consume, or charge from the grid, the ReactiveStrategy should also change.
  • If grid is lost, the system should back up as expected (5. Configuration)

OK so close to 24 hours in and this simple strategy seems to be working great…

Prior to adding this automation, notice the idle draw and SOC decline overnight:


Now, with the automation setting /Settings/CGwacs/MaxDischargePower to 0 when /DynamicEss/ReactiveStrategy is either 9 or 15 (scheduled idle):


  • The current is basically zero and the SOC barely dropped.
  • There were a few blips in current draw as the BMS SOC slightly fluctuated overnight. I believe this caused DESS to self-consume briefly, to bring SOC back on plan (which is another good outcome, as the automation still allows DESS to do these fine adjustments).
  • System started self-consuming normally in the morning when PV started producing.

Given tomorrow is Monday I will see whether this still allows DESS to charge ahead of the peak period.

OK so another day with no problems! :slight_smile:

To understand why this works a bit better I dug into the Venus source. Here’s the idle() function DESS calls:

DESS sets MaxDischargePower to a minimum of 1, which seems to keep grid feed in active for DC PV (based on the comment). The work-around I suggest above overrides that with 0, which disables grid feed in.

So in my case with only AC PV, I don’t think there are any ill consequences. Those with DC PV may want to build some additional logic.