Allowing for large ripple current on DC cabling in system design
When designing the system, I did not read the Multiplus manual in sufficient detail to notice the recommendation for 70mm2 DC cabling, so I sized the cables and the MCB for the nominal DC currents. It turns out that there are surprisingly large AC ripple currents on the DC cabling so the RMS current is much higher than the nominal current. You need to be aware of this when designing, otherwise things end up underspecced.
Here is a pic showing the DC-side current (blue) and the AC voltage (red). The current was about 82A nominal, but as you can see it’s actually got over 80A of ripple too (at 100Hz), giving an RMS current of about 105A.
My system diagram
System:
So the design current (4.4kW at nominal 48V) was 91A. 35mm2 cable is rated for 245A so that seemed fine, and also the MPPT terminals max out at 35mm2. However the measured current at 4.3kW (52.6V) was 82A DC, and 67A AC, giving an overall RMS current of 106A (quite a lot more than 91A!)
Given that design current a 100A givenergy MCB as a backup battery cable protection/isolator seemed appropriate. However, given the real RMS current of 106A, that (unsurprisingly) tripped after 28mins.
After 1.5 hours at ~4.2kW the breaker got up to 54C, and the cabling 39C, which is rather too toasty. I calculate a voltage drop of 0.57V and a power loss of about 60W. The voltage drop was measured at 0.5V, so that’s confirmed.
The Wiring Guide does talk about ripple voltages, but I understood that to be saying that if the wires were too thin ripple voltages could be too high, when the actual issue is that the operation of the inverter generates large ripple currents, and the wires+ancilliaries have to be sized to accommodate them. It could be clearer IMHO.
My cables are 4.5m from MPII to battery, so that’s ~0.65V drop over the 9m loop at122A RMS (max 5kW discharge) and 80W (1.5%) heating loss.
Section 4.3 in the MPII manual ([4. Installation]) recommends 70mm2 for 0-5m cables and 120mm2 for 5-10m. How are these numbers arrived at? (That does mean 70mm2 for my 4.5m cables (i.e. 9m loop), right? 120mm2 (the recommendation for 5-10m) seems bonkers). 35mm2 is already well within the ‘<2.5% voltage drop’, and the ripple voltage pre-alarm limit of 3V. Doubling up those cables would change voltage drop to 0.32V, and halve power loss to 40W.
The Victron toolkit app says 50V DC @122A over 9m causes 2.7% voltage drop in 35mm2, 1.4% in 70mm2, which is nearly twice as much as I calculated. Can anyone explain that discrepancy (does the toolkit use total wire length or one-way wire lengths?)
Ah, the Wiring guide, section 4 DC wiring uses a voltage drop of 0.259V to produce a table of current limits for a given cable. That gives only 53A for 35mm2 over 9m, and 109A for 70mm2 over 9m. Not clear if those are nominal DC A or RMS A? And where does that 0.259V come from? It seems a little arbitrary, but presumably there is a reason? Is this 0.259V the way that the recommended cable sizes are derived? Why this voltage?
It also has a section on Ripple Voltage (section 2), but that’s largely talked about in voltage terms/limits, not current. I’ve not seen any ripple voltage alarms so that appears to be within spec. Measuring the AC RMS voltage at the inverter I get 109.4V, and 110.7V at the battery end at 4.4kW (94A) discharge. Is that high, or expected? I am not getting any ripple voltage alarms.
Adding a 2nd 35mm2 cable would be £78, replacing with 70mm2 cable would be £162 (copper is expensive!). In simple cable-losses terms this would save about £15/yr. Is there also a gain in inverter efficiency, or any other considerations? A 10-year payback seems marginal. Annoyingly there are two holes through a brick wall which won’t quite fit a 2nd 35mm2 cable, so the cheaper option would require removing the inverter and drilling more/bigger holes.
So, what is the correct procedure for sizing cables? I have a 3-legged star topology with the MPPT (250/70) on one arm, the MPII inverter/charger on another, and the battery on a 3rd. Each of these legs has different peak load considerations.
  1. MPPT arm. 35mm2 terminals. No ripple currents. 70A max current. So 35mm2 cable is fine.
  2. Battery arm. Batt peak possible current is 180A. But max load limited by inverter out (5KVA, ~91A) and MPPT in (70A) (but those cannot be additive, right, only subtractive if both running at once?). Do I need to consider inverter (MP2 48/5000) momentary peak power of 9kW? I presume only steady current of nominal 5kW, which at low battery voltage could be 96A, except with ripple it’s really 122A RMS. 35mm2 (240A spec, or 162A according to Eland cables spec) should be fine, but are getting a bit warm. The MPII manual says 70mm2. Not entirely clear why.
  3. Inverter arm. Is this just the same as the battery arm, or different?
What fuse sizes should be on these arms?
So I’m a bit confused about all this now. I should probably just go buy some 70mm2 cable and a pair of busbars to connect it up, but I’d like to understand how things are calculated first. It would also be good to know if these ripple currents are typical.
Everything is working OK at the moment now I’ve removed the underspecced MCB. The cabling gets a bit warmer than is ideal, but not enough to worry about.
If ripple is too high, it will alarm or shut down. There is a VRM widget to measure ripple. I have a 200A MCB and 2x 35mm cable. Ripple is low. Also, if it’s too high the battery will micro cycle and this could reduce its lifespan. Not sure if there is any real science or calculations from Victron. Most likely real world testing.
To calculate the ripple you need to know the battery internal resistance, cabling resistance and capacitor bank details on the inverter input as a minimum. Just go with the empirical sizing, it is in the manual for a reason.
It’s not alarming, so presumably ripple is not ‘too high’ (which seems to be defined as 3V). But I measured 160A peak-peak, or 109A RMS. That feels ‘high’ to me, but I don’t know what ‘normal’ is for these systems.
I can’t find a ‘ripple’ widget under either ‘VE Bus System’ nor ‘Gateway’. Where might I find it? I did look in the dbus-spy values for a ‘Ripple’ reading but did not find one there either.
Unfortunately there are good physical reasons of space constraint why the Multiplus II and battery are in different locations either side of a doorway. The MPII is in the same cupboard as the rest of the electrics to make wiring up the grid backup (and import/export CT clamp) straightforward. There is not room for the battery in there.
I was aware that they should not be too far apart, but had not quite appreciated that even ‘2m apart (with a doorway to get over)’ is a bit far, and ‘right next to each other’ is desirable. It’s not impossible to change but it would be a pile of work. Buying some fatter wire is a lot easier.
I periodically check the widget. I think the shutdown is 2.5V for 5 seconds and 3V hard shutdown. I rarely see anything over 0.3V sits around 0.2V.
OK. I think you must have defined that yourself as a custom widget. It’s not in the default list. And indeed if I define a new widget, one of the values I can display is ‘VE Bus Voltage ripple - unit 1’. So now I have a ripple widget. Cool. I guess this is an outcome of the feature request in Feature request - DC Ripple Widget on Portal - VictronEnergy back in 2020
It’s typically under 0.2V, but on a good sunny day it wobbles up to 0.4-0.5V, and gets up to nearly 0.8V during 4kW discharge. So we are quite a long way off the 3V warning or 5V disconnection.
Just to follow up: I finally got round to upgrading my battery<->inverter cabling from 35mm2 to 70mm2 in line with the manual. It now gets much less hot (just gently warm during 3hrs max discharge rather than quite toasty). So I have at least reduced the losses from cable-heatings, although those would take a very long time to pay for the £170 odd of the upgrade.
Ripple has reduced slightly, but nothing like as much as I expected. Ripple during peak discharge is down from maybe 0.8V to 0.7V, but idle ripple (around 0.1V) isn’t obviously much different from before. I’ve only got one day’s data so far so the error bars remain high.
Good evening,
See this topic,
Read it carefully and if questions, please ask.
Regards, Jeroen.