AGM batteries swelling – clarification on capacity and charging settings

Hi everyone,

Quick clarification regarding my previous post:

The BMV is currently set to 440Ah because two batteries were disconnected after swelling was observed.
Originally the bank was 6 × 110Ah AGM (660Ah total), all in parallel.

Even with the reduced 440Ah bank, the remaining AGM batteries are showing signs of swelling.

Charging setup remains:

  • 3 × Victron MPPTs
  • Victron MultiPlus 3000W
  • Absorption: 14.40V
  • Float: 13.80V
  • Equalization disabled
  • Temperature compensation: -16.2 mV/°C

Batteries are installed in a warm / tropical environment and usually reach 100% SOC daily.

Given this, I’m trying to confirm whether:

  • These voltages are simply too high for sealed AGM in hot climates over long periods
  • Absorption time (with multiple MPPTs) could be excessive
  • A lower float and/or absorption voltage would significantly improve AGM lifespan

Appreciate any insights or recommended “safe” AGM settings.

Its important to know if this is actually correct for your batteries. And then also have a temp sensor on the ve bus as well (it comes with the unit) and make sure it is working.

Second thing is to check the C rating if the batteries and that has been exceeded as well as make sure excess bulk charging prevention is enabled.

I am not a fan of daisy chain set ups. But it seems even the middle one is having issues.

Could just be the heat. By warm- what temperatures do you mean?

You look like you have Victron AGM, I had Victron AGM before swapping to Victron Lithium. I used a temperature compensation of -24.5mV/C for 12V batteries taken from one of the Victron AGM datasheets or manuals and had a temperature sensor on the batteries, do not rely on the one in the MPPT and make sure DVCC and STS is enabled based on the correct sensor. Also I suggest that you would be better with a lower float, say 13.5V. A lower absorption may be advantageous with large numbers of batteries in parallel.

The one issue seen in boats is alternator charging from stock alternators with 14.4-14.6V regulators, there is no float so they get overcharged. If this applies you need an external regulator.

Hot AGMs see an issue where the hotter they get the lower the resistance, so more current flows generating more heat. Sometimes tail current is never reached.

Had the same issue. No help whatsoever from the dealer and only forwarding of emails by Victron Support.

They have great products but need to significantly improve their customer service.

Is this a current issue, or are those old photos from a prior issue?
If current, then yes, based on the serial number that’s 2 to 3 years out of warranty by now, so while I can commiserate with wishing for a contact back from the dealer, I’m not terribly surprised the dealer isn’t rushing to make contact - there wouldn’t be much for them to do in this case.

I had been communicating with the distributor for months. Prior to the failure, the battery temperatures were steadily increasing and I was concerned. I have 3 additional 230AH AGM that were all purchased and installed by a certified Victron installer at the same time. The bank is configured with a Multiplus II, Lynx Power In, Lynx 1000 Shunt, Lynx Distributor, Victron MPPT, CerboGX Orion Dc to Dc charger.

To be clear, I love the products but the service is poor. The installer was also not very competent as I found out following a survey.

Ah, that’s a drag to hear. Unfortunately “certified Victron installer” doesn’t really mean anything (sounds good tho) and we see many so-called “professionals” that may well be professionals at something, but certainly not electrical installation. Possibly excellent plumbers, I suppose.

AGM batteries only have a 2-year warranty and I just saw the HQ2151 SN, which means at least that one was manufactured about 5 years ago, so a bit beyond its time in any case.

Victron doesn’t sell to the consumer, so all consumer support always comes from the distributor and/or installer, not Victron themselves; that’s always been the case and will most likely remain so. Sadly, distributors and installers come and go and it’s sometimes challenging, especially after a couple years, to get meaningful resolutions. Best of fortune!