Just wanting to know if anyone out there has this unit set up with there 48V solar system. Seeking feedback AERL EG 600 new release does it work with a Victron 250/100 MPPT and Victron Multiplus 2 48/5000 notification on VRM using Alarm relay 1 and what’s involved getting it going and wiring it up. AERL EarthGuard EG-600 | Ground Fault Detection
AS/NZ 5033:2014 & AS/NZ 5139:2019
I was going to get the 250/100 then my installer told me it would be another $1000 for a GFD.
It’s not going to do a whole lot, just let you know there is some ingress in a panel, or there is a bad MC4. It just alarms.
I got the 450/100. It costs a little more but is worth it for galvanic isolation and ground fault detection. There is no protection if the 250/100 fails, the solar panel voltage will be seen on the battery, and the GFD will not let you know.