How to get my MP2 8000 system G100/2 compliant?

I am getting nowhere with my dealer, or trying to figure out how to get my MP2 8000 system G100/2 compliant. My dealer has sent several messages to Victron, and seems nobody can be bothered to get back to him with a solution.

Can you give some insight please as this is holding me up sending the commissioning forms to the DNO so I can start exporting.

If I had known this was going to be such a big problem, I would have chosen another company (I chose Victron because I will be installing solar in a Narrow Boat next year, and wanted to get some experience with Victron).

(This was moved by moderators from another topic opened by @kevdav100)

What are the needs of the G100?
How is it different to G99?

This has a different solution since you should not be running ess surely? But rather would need to use wind solar priority since it is a non fixed installation.?

Currently you will have to have an external G100/2 compliant reverse power relay fitted. The Victron was G100/1 compliant so you will be able to set export limitation to prevent the external G100/2 relay from operating. It will just be there as a fail safe but give you compliance. Its a clunky way of doing it but works. Victron will get it sorted but who’s guess when. Why they cant be bothered to communicate with customers and installers is beyond me. Would benefit everyone.