hi I’ve got a panel between my 3 phase genset and the ac IN on my multiplus 2 48/15k ,three of them ,three phase .
I’ve got a switch , breaker ,and 300ma rcd In this panel . Was working ok for couple months ,but .lately the Rcd has been tripping.
It’s a type Ac 300ma .
That’s a lot of leakage .
Any ideas ?
Ludo
2
The last time i saw a 300mA rcd trip it was water in the panel.
Definitely no water in the panel ,clean install checked all wiring . It’s a type ac rcd
Ludo
4
Then check all phases one by one and go on from there.
Anf check that the ground relais are off in all mp’s