Who added a panel with switch fuses and rcd between Genset and multiplus 2 ?
You ?
Simply swap 2 of the outgoing OR incoming phases … no matter which one … then the rotating field changes
Yes … It could be that the rotating field is now set to ‘L’ … according to the country where it was built … Italy, for example, often has generators with an ‘L’ rotating field
The neutral and protective conductors should of course also be routed sensibly through the distribution board … as the condition BEFORE the distributor
I did it and it works . I can’t tell you how much I appreciate your help . It’s four days cloudy cold weather coming and we are off grid . You helped me and my family a lot .
BUT replace the 30ma FI with a 100ma or leave it out completely … it only annoys you unnecessarily because you don’t need ‘personal protection’ here, only device protection.
“kuddelmuddel” … a german word for ‘nice but slight disorder’
Surge protection in any case … 1+2 … yes … from DEHN or a similar one … and a good earthing at the generator !!! and on the distribution box !!! so that the surge protection can also discharge. otherwise it is useless … !!!
The more ‘earths’ in the system … generator , distribution board , house … the lower the total resistance of the earth electrode and the protective conductor. All safety devices that rely on this … including residual current circuit breakers … benefit from this.
Depending on where and how the generator is housed, surge protection must of course also be installed.
Should an ‘overvoltage event’ occur there, it is immediately discharged to earth … i.e. type 1 surge protection on the generator and at least 2 in the intermediate box … of course 1+2 is also possible if you can’t get it any other way.