So I had my Yamaha HS7 studio monitors (speakers) plugged into a 48/5000 Multiplus II on AC1 out.
I fired up a generator going into AC IN, came back and the speakers were rooted making a popping sound about 5 times a second from the woofers (sounds like the smart gun from aliens but faster)
One speaker is much worse (louder) than the other but they both have the same sound coming out of them even with no signal cable plugged in to them.
Does the Multiplus II just pass through generator power without any conditioning? I suspect it’s dirty generator that killed the monitors power supply or power amp.
Why isn’t my scarlett 2i2 gen4, yamaha mg06, shure mv7 or mini PC also rooted? SMPS vs whatever the HS7’s use?
What can I do to protect my devices in the future? UPS? Power conditioners? $700 worth of rooted speaker is not fun. Wish I’d known earlier.
If my diagnosis sounds about right, what other devices are sensitive to dirty power?
Is there any saved data on the Multiplus or VRM that logs voltage? Or should I go stick my multimeter into the generator?
Yes. They are not power correction devices. They try to synchronise to the incoming source. If the source is too unstable then it disconnects.
It is possible the other ones were doing a simlilar thing and stressing out the power supply the whole time and degrading it, this last connection was just the straw that broke the camels back.
It was either a voltage spike. Or a dodgy floating neutral as another possibility.
Potentially surge protection. But if you need clean power, never connecting to a dirty one is the ultimate solution. For some sites, we just have an inverter that charges off the generator. The main system just remains inverting and never connects to the bad generator or source.
Yeah it sucks big time. I could’ve got half a decent generator for what the speakers cost!
Is getting a separate charger kind of overkill? I’m trying to work out if I just have a REALLY bad one or if this will be a problem with most generators? I don’t really know what to look for in the world of generators/gensets? Is a genset a generator with an inverter built in? All I know is pure sine and modified sine, I’m sure there’s more to it.
I’m doing a new build and have asked the same question here if you care to have a look:
How would I set up a generator to JUST charge the batteries? I’ve got a lot of DC loads that would ‘feel’ the charge, no?
If there are good generators out there that don’t have these issues, that would be great. I’m honestly not sure though, generators aren’t in my wheelhouse yet
Thanks
Use a 48V charger like an ecoworthy 60A or 100A to charge the batteries directly from the generator or grid. Your devices will only ever see pure inverter power from the multiplus, as you would never use its charger/pass thru function.
There is an efficiency cost in this but well worth it imo.
Yeah I’ve been looking at chargers and they can get very expensive when they start hitting 100A
I should’ve said earlier (doesn’t make much difference) but I’m actually supplying a second installation from the 48/5000 - the second installation is running 12v batteries and a phoenix 12/2000 inverter. There are quite a few DC loads as well. So if I took the incoming AC from the 48v installation, that AC is dirty when the generator is running. If I got a 12v charger that does AC to DC it’ll solve the problem.
I’m borderline better off just getting a GOOD QUALITY 12v generator right? 'm sure they exist and I don’t mind spending $1500AUD - I just feel like getting a 12v charger that does 100A+ will get crazy expensive and ultimately have less utility than a 3000w honda or whatever it is. Or will all the generators be dirty?
I wish there was a way to have a dirty generator charge batteries while the batteries could serve clean power to DC loads at the same time.
At the risk of displeasing some people, I’m sharing a solution that I’ve personally tested and that works well while remaining relatively economical.
The principle is to use a conventional generator, with no particular requirements regarding the quality of its output voltage. The generator’s 230 V output is rectified using a correctly rated diode bridge (Graetz bridge), together with one or more electrolytic smoothing capacitors (from a few hundred to several thousand microfarads, with a rated voltage of at least 400 V).
This DC voltage then powers an old grid-tie inverter (preferably a model more than ten years old, often available at a low price on the second-hand market).
This inverter is connected to the Multiplus’s AC output. The Multiplus then provides a stable grid reference to which the grid-tie inverter synchronises. From the latter’s point of view, the Multiplus behaves like a conventional electricity grid.
The grid-tie inverter’s MPPT stage uses the DC voltage produced by rectifying the generator’s output and feeds its power into the Multiplus’s AC output. The Multiplus then uses this energy to power the loads and recharge the batteries.
Points to bear in mind:
Avoid excessive power levels.
The generator must not have a power rating equal to or greater than the amount the Multiplus can handle.
The grid-tie inverter should be kept to a reasonable size.
It is preferable not to continue charging the batteries to 100%, because as the battery approaches full charge, the Multiplus naturally reduces the power it draws.
It is important to understand that the grid-tie inverter will feed in all the power available from the generator. If the battery is full and consumption is low, the Multiplus still has to manage this surplus energy.
In my case, a 2.3–2.7 kVA generator combined with a 2 kW grid-tie inverter gives good results without needing to reduce engine speed.
One advantage of this method is that the sometimes poor quality of the voltage produced by certain generators becomes much less of a problem. Once rectified and smoothed, this energy is generally well accepted by the MPPT input of an old grid-tie inverter.
Of course, this remains an alternative setup that requires an understanding of the energy flows involved and the limitations of the equipment being used.
MultiPlus 48/5000: converts 230V AC to 48V DC (charging).
MultiPlus 48/5000: converts 48V DC to 230V AC (inverter).
MultiPlus 12/2000: converts 230V AC to 12V DC.
MultiPlus 12/2000: converts 12V DC to 230V AC.
Are we agreed on the chain?
In any case, here are the possible options:
Solution 1 (economical):*Switch off the loads downstream of the 48/5000 while charging (what’s backed up by the 12V system continues running on battery).
Solution 2 (redundancy): Put a 48V charger directly on the generator output (a second MultiPlus would do the job and serve as a spare in case the main one fails). The advantage is that you can use almost any generator and replace it on the fly if it fails.
Solution 3: Switch to a 48V DC generator (but what about communication with the BMS during charging?).
Off-topic questions, just out of curiosity:
Where are the MPPTs connected in this installation (12V or 48V bank)?
Where were the speakers connected?