What kind of batteries/BMS do you use? Activating all the DVCC options seems odd to me, thats not ususally the case for managed batteries, but still could be for some
I don’t use communication with battery BMS option at all. In my case it’s impossible (
Instead of this, I use Victron BMW monitor to operate correctly with battery, an it works a few years very well !!
As I wrote, it looks like system very insured by itself from battery overcurrent, and it came with 2 or 3 latest firmware updates.
It’s not a big deal, because undercurrent still useful, and can utilize up to 85% of sun power, it’s ok for running systems. Just information for others.
You don’t have a managed battery so the inverter charge algorithm is used.
Yet you have set a managed battery voltage limit in DVCC which does not apply to your use-case.
Showing charts of PV power won’t help much as you need to see what the battery voltage at the MPPT terminals is doing, this is usually a deciding factor in chargers throttling or stopping.
That wasn’t the question. Have you measured the voltage at each of the MPPT’s, inverters etc to confirm they all agree?
What battery monitor is set under the GX → settings → system settings → battery monitor? (be sure that auto mode isn’t selecting the wrong one).
This is a lithium battery right?
If so do you have a lithium charge profile loaded?
You have equalisation set which would normally be 0V on a lithium profile.
When 3phase Multi RS system riches 9kW sun power (which is 50% of maximum 18kW for this model) it sends command to MPPT RS turn off solar generation
2 x MPPT RS are slaves
3 x Multi RS system is master
I believe it is the thing
That’s why I think in this way:
earlier, 2 or 3 firmware updates before, first MPPT RS always was Group Master, second was Standalone, both of them can’t see sun power from Multi RS, and situation like this didn’t happen
Now, actual firmware, 2 x MPPT RS are slaves, it’s absolutely logical and reasonable, both of them now see sun power from Multi RS, which is great, and something in Master-Slave algorithm “tells” to MPPT RS slow down sun power after Multi RS rich 50% of maximum their Sun Power
or
~9-10 kW from network total power is maximum charge power for 2 x MPPT RS at this battery voltage, which can also “tells” them slow down Sun Power
2 x MPPT RS immediately turning off sun power, and system trying to limit charge current only for 3 Multi RS. And it’s working good, but looks like other devices in this case are “out of game” for some reasons (
Play a little with the Max charge current of each Multi RS.
You have it set to 75A now.
And when you enable the Limit Charge Current, the implementation of DVCC will do 3 x 75 = 225A.
Which is greater than the 200A current limit imposed on DVCC’s Limit charge current.
So it will disable on some conditions MPPT RSes, because how it distribute current to chargers.
It goes on the assumption that the Multi RSes, with their 75A, will manage the total.
When it’s off, it will try to maximize all it can.
Try to set it to 50, which will be 3 x 50 = 150 and see if the MPPT RS will turn on for the rest of 200-150 = 50A
As a conclusion, for this to not happen, if you enable the Limit Charge Current, you need to set it with 5% greater than the total charging capacities of all chargers. For example, if all have it on all at 75A, then 75 x 5 = 375, so you must set it to about 395A.
This is also because it doesn’t take into account the DC (!!) current needed for the AC conversion/loads, in order to subtract it from the DC production.
It’s working way better, now I can reach 170A of 200A total limit in combination of 48A charging current for each of 5 device, - of course I will play with it a couple of days (absorption faze happened)