3 phase Multi RS 17kW + 32kWh NKON ESS Pro (Enschede, Netherlands)

Finished our brand new setup last week. Still running tests but wanted to show the results so far on here.



  • 3x Multi RS Solar 6000

  • 2x 16kWh NKON ESS Pro battery

  • Class-T busbar for battery connections (225A t-class fuses)

  • Power-IN with 200A MEGA fuses for inverters

  • VM-75CT using CAN (image still using ETH for testing)

  • Dynamic ESS Enabled

  • 70mm2 DC cabling to inverters

  • 50mm2 DC cabling to batteries

  • System placed in isolated wooden shed

  • 26m AC cable to AC-IN (10mm2) C25A 300ma selective breaker

  • 26m AC cable AC-OUT1 back to the home C32A breaker

  • Hager SFT440 bypass switch


  • SMA Tri-power 5.0
  • 20x 290Wp

Very happy with the result :smiley:

Next up:
Multi RS Solar has 2 MPPT trackers per inverter, the roof above the shed and partly the flat roof above the garage can hold 12 more solar panels, so next project is adding 2 strings of 6x 465Wp PV direct DC into inverter → battery.

where did you get these Victron-blue cable channels? :slight_smile:

Isolated shed… but not fireproof, cladding the walls with fire resistance board like Knauf Diamond would be my first job.. here i have a battery room finished with 3 layers Knauf Diamond, smoke, heat and gasalarm and a emergency stop switch, (1x RS 6000, DIY batteries, DIY busbar)

Search for Hager BA6801000BLAUB. I’ve got mine from Elektramat.

thanks - didnt´t know they exist :slight_smile: perfect for the Hobvy of some

what i don´t understand: the sense of such a big installation?

We have here PV 25kWP , Battery 30kWh - only one single MP2- 3000 and a Huawai DC-Inverter to support charging

As everything is logged - i never saw any profit in larger systems

Partly because i want to be able to heat the house using a heatpump, charge the EV and use the induction cook top. But also being able to run the whole house when the grid goes offline. But i think it would be perfectly fine with a smaller system indeed :innocent:

there is to much money :slight_smile: but it is a hobby

I am blue … dabba di dabba da … :+1:

gooood job … … and OSB panels don’t catch fire that easily either :wink:

go go go for more PV :grinning_face:

Agree, 2 emergency stops on the way, one in the shed itself and the other inside the house. Smoke/heat alarms as well. And i’m planning to clad at least the back wall with 2 layers of Knauf gipsplaat.

Hey there, fellow Dutchman here!

Why did you use thinner dc wire for the batteries?

Seeing the DC amperage is devided for 3 inverters, those 3 cables take less amperage then your 2x 16KW battery system. You can also see that difference in your fusing. Using lower amp fusing for your inverter, versus the higher amp fuses for your battery packs.

I would rather use thicker wires for your batteries, and thinner wires for the inverters. I’m going to install a similar system, but with 3x multiplusII 4k5, and for the dc wiring I’m going all 70mm, because I just ordered it all in one go. But if I wanted to, I also could have used 50mm for the 3 multiplusses.

Good question :wink:

I ordered the NKON ESS Pro 16kWh batteries and they included 50mm2 cables. I had the same feeling as you described, and maybe will upgrade to the 70mm2 cable instead. But the 50mm2 should be just fine for the 150A per battery that the NKON’s can deliver.

True, makes sense…

But what doesn’t make sense is, why do you fuse the batteries at 225A? That’s too much for the 50mm cable I would think.

*edit just checked it, but internet says different things…

I’m going to fuse my (2x 16kw diy) battery packs with 200A fuses each. And use 150A mega fuses for the 3 inverters each

wouldn´t it make more sense to limit DC current in MP2 to a much lower value, save money - instead of spending it for the few minutes a day that much power is needed?

Fusing should take the weakest link into account. The wiring might be capable of handling a lot more amps, more than say a BMS or battery. In that case a higher fuse rating, matching the wires, makes no sense to me.

Hopefully with three sets of contacts. You could also apply a fireproof paint on the wood instead of using plasterboard.

How would you save money on limiting the amperage?

not to buy and pay for a system that could handle 3 ovens the same time just in case the power fails

Yup indeed, i am using the Schneider Electric Harmony XB4 with 3 contact elements for each emergency stop. Would fireproof paint also do the job enough you think? That would save me some time :wink:

edit: I think i’m going to place Fermacell to the wall behind the installation, and paint the direct wall parts next to it and a part of the roof above it with fire resistant paint. Thanks for pointing me in that direction :+1:

Good question, and a long answer :wink: I wanted to use the Victron T-Class Busbar which only supports T-Class fuses from 225A onwards. The BMS is limited to 150A for each battery so the fuse is there in case a short circuit occurs which will then be a multitude of 225A flowing through the fuse. Increasing the cable diameter will be the most elegant solution, i agree and i might do that in the future. Fusing the Multi RS units with 200A and connecting them by 70mm2 is what the Victron documentation recommends you to do, so i did.

Nice setup!

I’m trying to find those inverter 200A MEGA fuses, as a detailed pic of the PowerIn (like the T) is missing, where did you hide them ?

But my $1M question is: “Why on earth is there EMAT stuff everywhere in a setup like this ???”. Using any other decent brand (Hager, ABB, Eaton, pick your choice…) would be less than <1% of the budget.

Forget the fuses and larger wires, I would recommend to invest in a decent fire distinguisher (or two… :smiling_face_with_sunglasses: :fire_engine: )