1 My Solar Solution
1 x Victron Energy Quattro 48/8000 (Grid Tide – Single Fase)
1 x Cerbo GX
1 x Victron Energy RS450/100 Soler Charge Controler
1 x 48V Freedom Won 40/32 Lithium-Ion battery
1 x Yamaha EF6600 Convetional Generator with 2 x 16A Outles
8 x 345W Sunpower CPV Panels, S -25.88, Azimuth: North, Tilt Angle: 30 degres° (Needs to be upgraded by 3kW)
2 Requirement
Configure inverter to go off-grid and use genereator to supply power shortfall by syncing with the inverter. I cannot go off-grid without the generator synchronising with the inverter.
3 Problem
Generator does not sync with inverter. I will not be able go off-grid without the generator being able to provide power on those days where there is not enough solar radiation.
4 VE Configure 3 Configuration
4.1 TAB: General
System frequency 50Hz
Shore current 55.0 A
Overruled by remote checked
Secondary input shore current 10.0 A
Overruled by remote checked
Dynamic current limiter checked
State of charge when Bulk finished 95.0 %
Battery capacity 800 Ah
Charge efficiency 0.95
4.2 TAB: Grid
Country / grid code standard None: (feeding energy from DC to grid not allowed)
Accept wide input frequency range
(45-65 Hz) checked
AC low switch mains off 187 V
AC low switch mains on 194 V
AC high switch mains on 252 V
AC high switch mains off 257 V
UPS function unchecked
4.3 TAB: Inverter
PowerAssist checked
Assist current bost factor 1.0
Inverter output voltage 230 V
Ground rel y checked
Inverter DC shut-down voltage 48.00 V
Inverter DC restart voltage 54.60 V
Low DC alarm level 51.00 V
Do not restert after short-circuit
(VDE 2510-2 safety) unchecked
enable AES unchecked
4.4 TAB: Charger
Enable charger checked
Weak AC input unchecked
Stop after excessive bulk unchecked
Lithium batteries checked
Disable VSense
(for diagnostic purposes) unchecked
Configured for VE.Bus BMS unchecked
Charge curve Adaptive
Absorption voltage 55.80 V
Float voltage 55.80 V
Charge current 55 A
Repeated absorption time 1.00 Hr
Repeated absorption interval 7.00 Days
Maximum absorption time 1 Hr
4.5 TAB: Virtual switch
4.6 TAB: Usage
Virtual switch usage Do not use VS
4.7 TAB: Assistants
4.8 TAB: Assestant Configuration
Assistants not used
4.9 TAB: Advanced
limit internal charger to prioritize other energy sources unchecked
5 Observatiooooons
5.1 Last Sync Between Generator and Inverter
This table reflects that the generator did synchronize to the inverter a couple of times. I do not have a RVSC file from that time.
5.2 Generator Hz and Voltage
When measured with a multi-meter, the frequency is close to 50Hz and voltage is close to 230V.
5.3 Voltage at Inverter AC Input 2
Volts: 230
Hz: 50
5.4 ESS Optio are Still Displayed in Controls on VRM Dashboard
Despite no ESS Assistant being configured and / or loaded, it is still reflected in the Controls (from the VRM Dashboard), the ESS modes for Optimised Battery Life, Optimised Without Battery Life, Keep Batteries Charge, and External Control are displayed.