Wrong grid and Ac Out voltage in Quattro
Hello everyone,
I have this configuration:
  • 2 Quattro 15Kva in parallel (230V)
  • 60Kwh BYD LVL battery
  • 2 5Kw SolarEdge inverters in AC out coupling with 20KWh high voltage battery.
The problem is that the Quatro always indicate that they have between 6/7 volts less than what is actually in the system. I measure with an ammeter at the grid input, at the AC in input of the inverter, at the AC out output and in all systems it shows 230V, however the screen indicates 223V.
When the loads from de grid are high (at night for example to charge batteries) and the general voltage drops to about 200 Volts, the Quattro indicates about 194 volts and disconnects from the grid. I have a voltage rectifier (one that makes a 23 volt jump) at the input of the inverter but it only comes into operation below 200 Volts but the Quattro disconnects from the grid since it thinks it is below 195V
These have been happening for a couple of months, before I didn’t have that difference.
Note: The entire system is updated to the latest firmwares.
Try fit an external meter it will be a much more accurate reading then.
I installed an external meter a few days ago and the problem persists as the Quattro continues to detect the voltage incorrectly and disconnects from the grid.
Hi @gorkamayoz
The Quattro has two AC voltage readings, one for AC input and the other for AC output.
Are these reading the same voltage when the AC input is connected? (They should)
If you disconnect the AC input supply, does the AC output voltage reading the Quattro show an accurate 230V?
In all cases also check and confirm the readings with your external voltmeter meter on the AC connection points on the inverter, not at a switch or some other point after connection.
Yes, are the same
accurate 230V?
Yes
Yes, I confirm, when I have 230 volts at the input and output connection points of the Quattro, the Quattro reads about 224V
I took these two photos tonight at the same time when the grid loads was high.
There are many strange things in the Quattro measurements, intensity and voltage are wrong…
I took these 2 new photos this morning without loads from the grid.
Good morning,
After several months of running hundreds of tests, yesterday I think I found the problem. As I mentioned in the first post, my system consists of two 15kVA Quatro inverters in parallel. One is a 2022 and the other a 2024. I set the 2024 as the master and the old one as the slave. Yesterday I tried reversing this, and to my surprise, the voltage measurements were correct again. I think that, in a parallel system, the voltage measurement is estimated from the master inverter, and I think the new inverter has a problem and is measuring incorrectly. However, when the old inverter is set as the master, the entire system measures correctly.