I have a couple of systems in the field that are experiencing random shutdowns of their inverters. Everything else at the time seems to be “nominal”. Often there is no significant load. Mostly seems to be MultiPlus-II. The systems have had CAN bus cabling checked & replaced. CAN errors and actual BMS errors don’t appear to be a cause. They have had replacement GX units. Sometimes the VE.Bus state changes in the VRM history; sometimes it does not. The systems are otherwise reliable for days or weeks between events and perform under load. Here is an example:
I’m trying to come up with a plausible scenario for this.
I have historically seen similar shutdowns when an inverter goes into a low-battery alarm state because the BMS has “gone away” (equivalent to an MPPT error 67).
So I wonder if the inverters are falling over because the GX device has gone away for some reason (eg: reboot because of lost contact with VRM).
Do the inverters check periodically for BMS state, and fall over if that periodic check overlaps with a GX device reboot? Or do they reset a watchdog each time the BMS data arrives, and then, if the GX device hangs up or crashes for some length of time, then the inverter shuts down?
I have seen the same pattern on a few sites, and a brief monitoring device restart on its own rarely explains it, because the BMS lost alarm normally waits longer than a reboot takes. I would look for something that interrupts the battery data for longer, or makes it look invalid for a moment.
First check whether the inverters log an alarm just before each shutdown, or simply go to off. If there is no alarm, a short DC voltage dip at the inverter terminals under a load step is worth ruling out, even with little load showing, because it is often too fast to appear in the history.
Then compare the event times against the device’s reboot or watchdog records and its uptime. If shutdowns line up with restarts that lasted unusually long, that points to the data timeout. If they don’t, I would look at the DC side and the battery’s own logs instead.
There are no VE.Bus Warnings or Alarms before the shutdown. More to the point, sometimes the inverter state is not captured as being off - even though it definitely is - it’s just not there. For this reason, I was pointing fingers at a faulty GX units and/or VRM reboots until I got a few instances where everything but the inverter was on and generating changing log data during the inverter shutdown (and I realise the low battery due to BMS lost theory doesn’t really work for that).
You and @nickdb both suggest that “BMS lost” is a timeout, rather than a periodic check… I hope that’s the case because if it is checking on a fixed interval, then very occasionally that might intersect with a very busy or rebooting GX device.
I don’t believe there are any major DC hassles - the systems run fine under much larger loads and don’t appear to have discrepancies in DC measurements across devices (eg: the battery voltage measurement vs VE.Bus vs MPPT) that would usually indicate a bad crimp or something (and no DC ripple warnings). CAN cabling has been checked as I mentioned.