Virtual switch, but also be able to manually turn on/off

I am using Virtual switch on a multiplus II, and I have it configured to turn on grid input when battery SOC drops under a certain amount, or when power draw exceeds a certain amount of watts.

This works for most use-cases, but there are certain situations when I want to manually turn on grid input, ideally from the interface. Is there a way to do this?

No there is not.

But there are other ways to mimick Virtual Switch or ignore AC and have an override.

Interesting, but I do not see relay 1 in settings / devices / GX internal relays list. I only see relay 2 there

Do you have it assigned to anything?
Try settings - integrations

is it the Function relay 1? I see it set to “Alarm relay”. If I change it to Genset, the it appears under devices as Genset

Yes. Assignment is important there