I have a question regarding the energy measurements given in VRM. In specific:
On a typical day - say Nov 17 - my installation generated 4.2kw of solar and consumed 2.4kw ac loads. Battery (4.8kwh) went from 39% to 61% in these 24h.
The battery should then have 3.4-1.6=1.8kw for charging. For a 4.8kwh battery, this represents 37.5%. Instead, the battery increased 61-39=22%, which represents a difference of nearly 40%, or 0.75kw!
Example; The battery has charged 3.4kWh at let’s say 90% efficiency = 3.06kWh in the battery. Then discharged 1.6kWh to the loads at again 90% efficiency is about 1.78kWh from the battery. This leaves 1.28kWh in the battery, or about 26% charge in this example.
There is also standby loss, meaning the inverter will use power even when it’s not inverting.
Efficiency seems indeed very low, even considering heat loss. Assuming 90% charge/discharge efficiency as you suggested and inverter efficiency (rated 96%) there is still a good 10% energy loss unaccounted for…any ideas?
Battery has reached 100% last times on the 21st and 22nd November…recently then…battery health is also 100%, it was installed in August this year. Whole system is pretty new…