Variable Inverter charge rate dependant on site load/SOC

Hi. Looking at feasibility of using Dynamic ESS module and/or DVCC function to give a variable charge rate control to the inverters in three phase setup, (dependant upon site loads/battery storage State of Charge) to ensure maximum loading for Stage 5 generator on A.C. Input. Existing system set up with 3 x 10kv or 15kv Victron inverters, Cerbo controller, utilising 3 Phase generator input for charging and excess load.
Is this achievable with this or any other available Victron Hardware on the Cerbo platform.
Thanks in advance, Jon B

@JonB
Are you running an ess programmed system?
The inverters have power control as a feature already. It is governed by the input current limit.

Rate of charge is governed by load (given priority), what ever is left over is used to charge.
Papers here and here

Hi Alex ,
Thank you for taking the time to reply. No we are not using ESS currently, but this should prove useful! We will go through your papers and do some testing.
Thanks again Jon B