I’ve designed this Victron system with a MCS electrician. We loosely built using the UK Offgrid Systems Cube system as a template. Which as the name says was an off grid system. The design we’ve created is an on grid system. I look forward to getting your feedback.

https://cloud-object-storage-cos-standard-djc.s3.eu-gb.cloud-object-storage.appdomain.cloud/three-phase-ess.png

System Overview:

A three-phase Energy Storage System (ESS) using Victron components, configured for zero export initially, with a total battery capacity of 35kWh (48V nominal). The system is designed for robust performance, safety, and compliance with UK regulations.

1. DC Power System & Batteries

  • Battery Bank:

  • Chemistry: Lithium Titanate Oxide (LTO).

  • Configuration: Fifteen 48V/50Ah batteries arranged in three independent 5-battery strings.

  • Safety: Each individual battery is protected by a 100A marine fuse and a DC 125A isolator switch.

  • DC Wiring & Distribution:

  • String Level: Each battery string uses 35mm² cables of equal length to connect to its own dedicated copper busbar.

  • Main DC Bus: The three string busbars are connected to a central set of large copper busbars using 95mm² cables.

  • Protection: Each 95mm² positive cable is protected by a 250A Class-T fuse.

  • Monitoring: A Victron PowerShunt on the main negative busbar provides state-of-charge and power data to the Cerbo GX.

  • Inverters/Chargers:

  • Units: Three Victron Quattro 48/10000/140 inverters.

  • Connection: Each Quattro is connected to the main DC busbars via 120mm² cables.

  • Protection: Each positive cable to a Quattro is secured with a 400A Mega fuse and a high-current DC switch.

2. AC Power Path & Grid Connection

  • AC Input (Grid Side):

  • Grid Connection: 25mm² cable enters a 125A 4-pole isolator.

  • Grid Monitoring: A ZIEHL UFR1001E monitor controls an ABB AF65-30-00-13 contactor based on grid health.

  • Distribution: Power flows to a distribution board with 63A MCBs, which feed the three Quattro inverters via 16mm² cables.

  • Energy Metering: A Victron ET340 energy meter, with Carlo Gavazzi TAD3 current transformers (CTs) on each phase, communicates with the Cerbo GX for ESS control.

  • AC Output (Load Side):

  • Safety Monitoring: A Bender RCM423 insulation monitor, with Siemens CTs and a co-located Bender W35 core balance CT, provides earth fault and RCD protection.

  • Control: Power passes through an ABB AF52 contactor.

  • Final Distribution & Protection: The output is secured by a 63A 3-pole MCB, a MK Sentry surge protection device (SPD), and a final 63A isolator before connecting to the house loads.

  • System-Wide AC Notes:

  • All three-phase wiring maintains correct phase sequence (L1, L2, L3) and uses UK colour-coding.

  • All AC neutral conductors are consolidated onto a single copper busbar for efficient distribution.

3. Control, Monitoring & Configuration

  • System Controller: Victron Cerbo GX Mk2.

  • Operational Mode: Configured for Energy Storage System (ESS) with Zero Export to the grid.

  • Monitoring:

  • Victron VRM: Enabled for remote monitoring via the VRM app with push notifications.

  • CT Orientation:

  • Grid CTs (Carlo Gavazzi): “K” mark facing towards the grid.

  • Load CTs (Siemens/Bender): “K” mark facing towards the house loads.

4. Mechanical & Safety Compliance

  • Cable Management: All cables are securely fastened with P-clips at ~150mm intervals, including support for bends.

  • Terminations:

  • High-Current (Lynx): M10 bolts torqued to 30 Nm.

  • Standard Busbars: M8 bolts torqued to 18 Nm.

  • UK Compliance:

  • Export Limit: System export power is hard-limited to 16.5kW.

  • Grid Draw: The design ensures total draw from the grid remains below the UK standard 100A fuse limit

Are you 3xpecting long runs to the dc bus bar? 2x 95mm² will work better.

I’m planning to keep the final DC run as short as possible, probably less than 1.5m to each inverter.

Another question. Is it possible for me to get the design professionally verified at a reasonable price. My friend has recently got his MCS certification and this is his first 3 phase design. We’ve verified the design against a number of AI systems and incorporated feedback and recommendations, but I don’t fully trust the judgement of AI systems. Can’t beat real human experiences!

It is probably best to use a local dealer. You can find a list on Victron Where to Buy

Yeah AI has a way to go before it can be relied on for this type of thing particularly if you don’t have the knowlege to evaluate ehat it is saying.