Unexpected Low Voltage Alerts

The installation is back on track again. No HW changes, no reasons found. Update to 3.64 went fluent without loosing any setup values including changes in etc/watchdog.conf survived. The Pylon min/max values did not come back with the update. Instead “internal failure” notifications. I had to reboot the master stack several times until its address enumerated in consecutive order. Then plugged in LV_Hub and all batteries were recognized by Venus immediately including all min and max values. I am also able to identify the rack position 010D what contains highest and lowest cell voltage. Convert hex to decimal while address count starts at 1 instead 0. The 010D battery has a disbalance at 100% SOC from 3,35 to 3,5V. Within 4 hours the passive balancer managed to reduce disbalance from 165mV to 155mV what is too slow. Maybe I have to take it out from the stack and balance separate over 24 hours.