The installation is back on track again. No HW changes, no reasons found. Update to 3.64 went fluent without loosing any setup values including changes in etc/watchdog.conf survived. The Pylon min/max values did not come back with the update. Instead “internal failure” notifications. I had to reboot the master stack several times until its address enumerated in consecutive order. Then plugged in LV_Hub and all batteries were recognized by Venus immediately including all min and max values. I am also able to identify the rack position 010D what contains highest and lowest cell voltage. Convert hex to decimal while address count starts at 1 instead 0. The 010D battery has a disbalance at 100% SOC from 3,35 to 3,5V. Within 4 hours the passive balancer managed to reduce disbalance from 165mV to 155mV what is too slow. Maybe I have to take it out from the stack and balance separate over 24 hours.