Good afternoon everyone,
Just looking for some insight from the community. We recently upgraded our off-grid setup to a 48V system using four 100Ah WattCycle LiFePO4 batteries wired in series. I also added a LiTime 48V active balancer. All the standard steps were followed during commissioning : the batteries were fully charged, then paralleled for 24 hours to equalize, and then connected in series.
Everything worked great while I was on site for a couple weeks. The balancer kicked in during each charge cycle, and I’d occasionally see up to 3–4% SoC difference between batteries. But within 30 minutes after the charge controller stopped, all four batteries would level out in both SoC and voltage. This was confirmed through the BMS Bluetooth apps.
However, this morning I got a call from a family member currently at the off-grid site. They had a blackout last night after six days of no sun. The main battery breaker tripped, and lights went out suddenly. I suspected the batteries had fully discharged.
After some troubleshooting, it turns out three batteries were sitting at around 0% (about 11.1V), while the fourth was showing 60% SoC and 13.2V, which seems very odd, especially with an active balancer in place. I advised not to flip the battery breaker back on and to give the balancer time to work.
By this afternoon, the situation improved slightly. The three low batteries were at ~2% SoC (12.3V), and the high one remained at 60%. They’re heading into town tomorrow to grab a lithium charger and will individually top up each battery to 100% before reconnecting them in series.
A few questions for you guys :
Any idea how this imbalance happened despite the balancer?
Is it safe to reuse these batteries in series once they’re all fully charged again?
Is there a quicker or safer way to recover from this situation in the future?
Appreciate any thoughts.
For reference, these are the system specs, should more information be required, please feel free to ask and I will fill you in.
1× Renogy Rover 60A (soon to be replaced with a Victron SmartSolar MPPT 150/45 in July)
4× 105Ah Wattcycle BT Mini batteries
1× 48V LiTime balancer
1× Victron Cerbo GX MK2 (to be added in July)
1× Victron SmartShunt (to be added in July)
1× Victron 48/800 120V Phoenix Inverter
1x Meanwell 500 W 18-70 VDC / 12 VDC converter
- All breakers are two pole breakers for both positive and negative.