System Component Layout Question
Greetings All,
I have a cabinet I am building using a MultiPlus 12/500/20 unit and have also purchased a Battery Protect 12/24 65A and the 300A SmartShunt.
The idea is to have shore power come in and down to charge the battery bank of 4 batteries in parallel to equal 12vdc at 300ah.
From the batteries I was planning on connecting them to bus bars. I need to ensure if the load runs on battery to a pre-determined limit that the battery protect basically shuts down everything.
Do I need both the Smart Shunt and the Battery Protect or do I only need the Smart Shunt or Battery Protect?
The whole cabinet is technically a critical load so perhaps getting the Battery Protect is pointless beyond seeing the CerboGX and modem.
For the Smart Shunt should I connect lets say negative on battery 1 and the positive on battery 4 or should I just connect it to the bus bar where the other systems will pull some power from as I have both DC and AC loads…..
Can someone shed the light on this for me?
TIA
Do you really need a BP? The inverter will have a low voltage disconnect.
The shunt is worth it. One end is connected to the battery negative, to the other end the consumer/system negatives for probably the domestic negatives. A second battery, engine, voltage can be monitored as well.
I have my shunt bolted to a large busbar - a 25mm x 6mm x 400mm copper bar to which all DC negatives are terminated. It is also the vessel grounding point and bolted to the steel hull. All the AC grounds terminate on it as well.
If you use the battery protect you must not power the inverter from this. The manual shows how it needs to control the inverter remote port. Agree with post above, the inverter should have low voltage shutdown amyway.
So if that is the case for the bus bars, if the unit can push 500va but my draw on 12vdc is only lets say 10A, do I need a larger bus bar than 150A rated?
Thanks!
150A bus bar would be OK, you would need to fuse the battery to bus bar line accordingly. The only concern is that the 150A busbar has a large enough terminal for the inverter, no good if it has 5 x 30A small terminals. The inverter manual will recommend cable and fuse size.
Sorry was restructuring my question @pwfarnell as you wrote this……
So if that is the case for the bus bars, if the unit can push 500va is that on the AC side and not DC side? Do I need a larger bus bar than 150A rated on the DC side since I am going from the output of the inverter VAC to an outlet?
I am taking shore power in 120VAC and then outputting from the inverter to an outlet for this use case because I only have 2 AC devices, and the battery charges at 20A load, so does this mean that the battery disconnect can be rated at 20A?
How about the VAC outlet? would a 5-15 or a 20A outlet be ok to wire in-line for the VAC output?
Thanks!
The inverter will output 500VA ac, so in normal operation it could draw say 600W DC, so at 12V, that is 50A. There will be higher peak loads and the manual gives a fuse size of 125A. If you have no large DC loads you should be OK with 150A bus bars.
For your ac outlets, normally will be below 5A, but your unit can passthrough 16A on top of this so your output system can be designed for a higher output if you wish. The manual should provide info.
That confirms some of what I thought. So for the AC side do you think a 20A outlet would be the safe bet? I know a 20A circuit usually delivers right below that. I am afraid a 5-15 outlet may trip or burn up if it can hit 16A….. Thoughts?
If you have a smaller outlet then you have to have a breaker smaller than the max throughput. 20A seems like a sweet spot.