Hey folks,
I wanted to make sure my scheme to use victron quattros to provide 480V 3 phase from batteries (and maybe more), while charging from split phase, is possible/makes sense.
A bunch of context:
I am in the US and have a large home shop where ~everything is run 480V 3 phase. Lots of significant (for a home shop) HP machines (metalworking CNC, woodworking CNC, etc). I currently use about 40KVA of 480v 3 phase. I can actually get utility 230V 3 phase, but not at a reasonable cost (it would be about 60-75k). Instead, I have 800 amp split phase service (which had cost about $1500 to have done). We are at the literal end of the line for power service, so ~any outage anywhere on our line always affects us.
The shop 3 phase is currently produced from 225amp split phase through the following scheme:
230V Split Phase → 230V Isolation Transformer[1] → 54KVA Phase Perfect → 230V 3 phase to 480V step up transformer.
The phase perfect is nearing the end of it’s life. Replacement is about 20-25k. Simultaneously, i was also exploring both battery backups for the house/shop, and doing peak demand shaving (because of my TOU tariff, peak demand shaving would save me about 300-500 a month, more in summer months), plus maybe some solar (we have slate roofs, can’t do roof solar, but i have other areas).
I was thinking of getting a 50kwh (or whatever, depending on how long we want house/everything to run without charging) battery cabinet, use 1 quattro 277 inverters per phase to provide 480V 3 phase from it, and charge the batteries at night from the grid 230v split phase. Will this work? It looks like it should by the manuals, and messing about with the demo systems in ve configure, it seems like as long as i tell them not to switch as a group, this should work.
It also looks like, as long i’m careful not to exceed max charge/discharge currents, and am careful about wiring, i could also hook up inverters to provide 230v split phase from the same battery cabinets and interpose it between the home and the grid to provide peak demand shaving/battery backup for the home as well (and if needed, only charge the batteries from this part of the setup instead of from the 277 part, keeping the 277 part in inverter only mode)
But reality is sometimes different, so figured i would ask if this is possible, and if there is a horrible downside i’m missing.
Efficiency wise, if the datasheets are correct, on the 480v side, this is actually a bit more efficient than my current system because of my current transformer losses/etc.
You can also assume i’ve done the cost math on all of this, and because of how much electricity we use/time of use tariffs, the payback period would be quite short (<5 years at current costs). Compared to buying a new phase perfect, it’s basically a wash to buy inverters + battery pack, and it seems the longer i wait, the better the batteries + inverters come out cost wise.
[1] While the phase perfect is low THD output, it does couple plenty of noise onto the input at this size phase perfect. I’ve had long, drawn out discussions with phase perfect about this, using my fluke analyzer data to show them that it is their unit that causes it, and the end answer from them is “yes, and that sucks, such is life”. To avoid this affecting the house lights/etc, i currently use a 240->240 isolation transformer before the phase perfect.