Solar Gone to Idle After ESS setup, also loads gone to Critical

like this

I understand, so i can just link them within software.

HQ2250 and HQ2250 Phase 1
HQ2251 and HQ2149 Phase 2
HQ2046 and HQ2049 Phase 3 (This one is my first unit, with software updating i thought be Ok)

Ok found issues in the config.
Battery capacity incorrectly set to 10AH on all systems and ESS assistants.
Phase 1,2 and 3 slaves - grid is limited to 9A and it has no grid code set, master is 31.5A (they must all be the same)
Phase 2 master - ESS assistant no battery capacity set
Phase 3 master - dynamic limiter is on, battery monitor is disabled, power assist enabled, inverter tab all incorrect for pylontech, charger tab incorrect absorption time (this inverter need a proper reconfigure)
Phase 3 slave - no ESS assistant.

You have a lot to correct here. Follow: Victron & Pylontech UP2500, US2000, US3000, US2000C, US3000C, US5000, US5000B, UF5000, Pelio-L, UP5000, Phantom-S, Force-L1 & L2 [Victron Energy]

No, they have to be wired onto the correct phases, then reconfigured.

ok. I think i can set all that, and then if i send you the config before i write it to the system?

yes sorry, they wired into correct phases as they will be incorrect on the phases.

Sure. But I have dogs to walk first.
Config is part of the issue, if it persists, you need to physically move inverters (after you measure them all by hand)

Thanks. i have 9 x US5000C and they say they 100ah so i put the setting to 900ah?

Sounds right

2nd Latest Config 14-6-2025.rvms (9.5 KB)

Looks good.
Let’s see how this works.

Each phase can draw up to 100A, hopefully that is within your rated supply?
(you can override this in the GX device setting)

Else you need to get your meter out and start shuffling inverters around.

Thanks Nick, i presume when you schedule a charge it just charges the batteries to the limit i set?

Indeed

not too sure how to PM , but you might want to rename your file as you have your street adress in it :stuck_out_tongue: