The SmartShunt should he working reasonable well. The discharge floor for lithium is typically 10% or 20%. If your system is going dead at 48% then you have some serious problems. Have you checked that each of the 12V batteries in series are balanced because one poor pack going off line because it is not balanced would be an issue. You really ought to do a monitored draw down if you are losing power at 48%. The other possibility is you have not wired the shunt up properly a d you have some power draw from the battery that is not being measured or you have a large zero error. See the manual for zero current calibration and this link for wiring.
Related topics
Topic | Replies | Views | Activity | |
---|---|---|---|---|
SmartShunt 300 not synced to batteries | 3 | 91 | 23 June 2025 | |
Smart Shunt (500A) Has 10-15% SOC variance regardless of settings changed | 2 | 47 | 5 August 2025 | |
Another trouble shunt | 2 | 62 | 28 July 2025 | |
Lynx Shunt | 11 | 90 | 28 May 2025 | |
Help with configuration that won't charge above 65% | 10 | 135 | 6 July 2025 |