I have set a 160W solar panel with a 136Ah Sunwind AGM battery. The recommended absorption voltage for this battery is 14,22V and float voltage 13,60V and I have set these values in the app. However the battery voltages are usually about 0,2V below set charge voltage values. Is this normal operation for the charge controller or is something wrong? Ambient temperature is about 23 - 24 celcius so the reason shouldn’t be the temperature compensation? Could anyone help me with this issue?
The 1W/0,1A load is always there. Just took the fuses out of the load and the 1W was still there. First I thought it was the controller using that 1 watts but it shoudln’t be that high right? It should be like 0,02A load for the controller if I remember correctly.
Just checked the battery terminals and the reading was 13,49 volts whilst the controller app reading was 13,42 volts for float voltage. Maybe I should increase the voltages by 0,2 volts then?
At 0.07v difference means the mppt is reading well. It is within margin of error. Nothing to worry about there.
But what that means then is its not the mppt that has an issue, but you have voltage drop over your cable. Maybe resistand in lug crimps or smalll gauge etc.
Either change the cable or increase the voltage to compensate.
If you look at your battery spec there should be an allowable 0.2 to 0.3v difference in charge voltages. At least most AGMs all that.
You can always switch the load ouput to always off if its not already set like that
I asked the battery manufacturer about the charge voltages. They said that it’s also completely fine to use 14,4V absorption and 13,8V float voltages on a normal solar panel system with a relatively small panel. So it shouldn’t be an issue if the actual charge voltages go near those values.
I checked all the connections and they should all be nice and tight. I have an automatic fuse next to the batterys positive terminal, so the voltage drop could be bacause of that. Or the gauge is simply too small? I have a 6mm2 gauge with a length of approx 1,5 - 2 meters between the battery and controller.
Its possible the resetting fuse is the issue they have pretty high resistance.
6mm² is ok for 20A. Maybe with the length as well it might also be a contributing factor.
Either way your 2 choices are
Redo the DC side to the battery
Compensate the volt drop with settings. The battery will reach the correct voltage at its terminals even though the mppt reads higher.