Hello together, I am encountering a situation where the Victron SmartShunt reports a discharging current, even though both the JK BMS and independent measurements indicate there should be none. So i have the electric water heating unit, full sun outside but PV is delivering 2.1kW but at the same time battery is “discharging” with 1920W which is not true.
Not really lots of information, but to me it looks like the pv minus from the mppts is connected directly to battery minus, not to the load-side of the shunt ?
Also you need to make sure your lug stacking has the low current connection on top of the high current ones. Check your negative there with the lug going to the shunt. As a further point is the cable there the same gauge as the cable feeding the inverters? Should it not be the sum of all the inverters it is feeding?
But just in case someone else comes along thinking they had the same issue and hasn’t made the same mistake, i though to add another possible point of troubleshooting.
Since @kta22 is set on improvements to his system the lug stack also needs attention.