Hi everyone,
I have a SmartSolar MPPT 150/100 VE.Can charge controller. At the moment, I’ve got 8 JA-Solar JAM60D42-525/LB panels connected to it, with the following specs:
Voc = 43.73 V
Vmp = 36.37 V
Isc = 15.21 A
Imp = 14.35 A
The panels are wired in a 2S4P configuration, so 8 panels in total, giving about 4,200 Wp. As you know, the SmartSolar MPPT 150/100 has a max short-circuit current (Isc) limit of 70 A. My current setup gives Isc = 4 × 15.21 A = 60.84 A — all good so far.
My question is: can I safely add one more string, so the setup becomes 2S5P (10 panels total, 5,250 Wp)?
In theory, that would exceed the controller’s Isc spec, since 5 × 15.21 A = 76.05 A.
However, I’ve noticed that Victron allows a bit of margin on this for the MPPT RS series — as long as the panels are wired correctly, since reverse polarity damage wouldn’t be covered by warranty anyway.
I’m planning to be extra careful with the wiring. I’m using a proper solar combiner box with fuses and protection for each string, so I’m not worried about connection mistakes or short-circuit risks on the PV side — that’s well protected.
What’s puzzling me is that even with the current setup, I’ve already seen panel operating currents higher than the theoretical Isc. I’ve seen charging currents around 65 A when the sun is really strong.
Can the actual charging current of the controller exceed the Isc value from the panel spec? I understand these peaks are temporary, but if I add a fifth string, I’ll definitely go over 70 A at times.
I also know I could add more panels by changing the wiring to 3S4P — that would give me 12 panels total and about 6,300 Wp. But I’d rather not go with 3S because my panels get some shading from trees, especially in winter when the sun is low. In that case, a 2S setup performs better than 3S.
P.S. Just to clarify regarding my battery voltage — I’m using Li-Ion NMC batteries in a 15S configuration. I charge them up to 61.50 V, which equals 4.10 V per cell.