I have a smaller DIY camper system install running for 3 years now. Still trying to find a way to maximize solar consumption for the times we are connected to grid and paying for power. It works well for our needs.
Iâm seeing the request to maximize solar over grid power often and many of the installs are RVs and boats which are specifically prohibited from using ESS.
The recent addition to prioritize alternate charging sources for DC loads doesnât help for AC loads.
Please Victron split out ESS functionality so that solar can have priority over the grid for mobile apps or qualify ESS for use with mobile apps as long as the grid code is set to none to prevent grid feed-in.
You can use a relay on the GX and the AC ignore function of the Multiplus to make the shore power behave like a generator.
This would maximise solar generation but also allow you to automatically or manually connect shore power to recharge batteries or supply loads beyond what the Multi can.
Why canât the System simply be run in ESS Mode? Connecting / Disconnecting Shore Power wouldnât be much difference to a grid loss at home, I assume?
Sure, it would automatically priorize bat usage over grid, but thatâs what desired, isnât it?
Forced charging could occur through charging schedules?
Or are there sustainable features that do not work along with ESS?
The challenge that I have run into with my smaller system is I can easily overload it and need to be able to accept AC base on power demand. In my previous attempts to use The Ignore AC Virtual Switch the Multiplus II only monitors the AC load on L1. If high draw loads are on L2 it can overload the system. I have looked at using generator start stop but not sure if that would see the total load of the system since it is run from the Cerbo?
Iâm sure it does see the whole load and easy to test. Just enable one relay as Generator Start/Stop then set the load conditions. Apply your test load and see if Cerbo engages the relay, donât need to have it actually connected to anything.
I had used ESS in my RV for quite some time, but I also have dual backfeed prevention devices. The reason I stopped is because ESS never played nicely with my generator. (I got tired of reconfiguring the multiâs every time I was travelling or plugging into shore power) Even with the ac source set to generator the MP2 would still âpolâ the ac input every so many seconds, which resulted in constant fluctuation of the ac. Not good for the generator or some of the ac components connected to the system. My little Honda doesnât seem to care but the big Kubota does not like it. I was under the impression that when the AC source was set to âgeneratorâ that the MP2 behavior would be changed to normal (disabled ESS) but that doesnât seem to be the case.
I know not exactly relevant to the OP, but something to keep in mind for those that may decide to experiment.
I have tried with LOM disabled and it still doesnât play well. I know itâs something to do with the ESS because the generator is smooth with ESS disabled. I think victron still needs to do a little work on this but I donât see that happening.
I set up start stop on the Cerbo and test loads on L1 and L2 and it work to indicate the Generator (connect to AC) worked. Now just need to wire to the multi plus and configure. Thanks! been lo0oking for a solution like this for a couple years.
Not sure why youâd say you âdonât see that happeningâ. Victron updates their inverterâs assistants on a very regular basis, not just firmware, but the ve.configure assistants too.
I say that because I brought up the issue a few times on the old forum and nobody at victron seemed interested in investigating further. Unless multiple users start reporting the same issue Victron is not likely to dedicate resources to it, which I wouldnât expect them to anyway, they have enough other things to focus on.
Just to be clear, I am not in any way bashing on Victron. They have to prioritize issues and I understand that.