I have 2 Skylla-IP65 12/70 that do not output 140A of charging as expected on my 12VDC system
I am interested in what I should be seeing or if I have an issue with the configuration below.
When the batteries are at 13VDC The 1+1 charger will go to 60-70A of charge while the (3) charger will hover around 6-8A of charge. This is far short of the expected 140A of total charge I should be seeing.
The chargers appear as a single charger when displayed on the Cerbo, this appears to be by design.
I have the following.
A Skylla-IP65 12/70 (1+1)
A Skylla-IP65 12/70 (3)
Devices are in a cool environment and are cool to the touch.
Both are connected to a Cerbo via VE.CAN in this simple config:
Cerbo — UTP-8 — Skylla-IP65 12/70 (1+1) — UTP-8 — Skylla-IP65 12/70 (3) — Terminator.
Settings are in table below.
Setting | 1+1 | 3+1 | Description
1 | ON | ON | POWER ON OFF
2 | 70 | 70 | MAXIMUM CHARGE CURRENT
3 | 12 | 12 | SYSTEM VOLTAGE
4 | 8 | 8 | CHARGE ALGORITHM
5 | 14.4 | 14.4 | ABSORPTION VOLTAGE
6 | 13.8 | 13.8 | FLOAT VOLTAGE
7 | 13.2 | 13.2 | STORAGE VOLTAGE
8 | 15.9 | 15.9 | EQUALIZATION VOLTAGE
9 | OFF | OFF | AUTOMATIC EQUALIZATION
10 | START | START | MANUAL EQUALIZATION
11 | 0 | 0 | RELAY MODE
12 | 11.6 | 11.6 | RELAY LOW VOLTAGE
13 | 12.0 | 12.0 | RELAY CLEAR LOW VOLTAGE
14 | 17.2 | 17.2 | RELAY HIGH VOLTAGE
15 | 16.7 | 16.7 | RELAY CLEAR HIGH VOLTAGE
18 | 0 | 0 | RELAY MINIMUM CLOSED TIME
19 | Y | Y | ADAPTIVE MODE
20 | -2.7 | -2.7 | TEMPERATURE COMPENSATION
22 | OFF | OFF | BULK TIME PROTECTION
23 | 8 | 8 | MAXIMUM ABSORPTION TIME
24 | OFF | OFF | STORAGE MODE
25 | 8.0 | 8.0 | MAXIMUM FLOAT TIME
26 | 1 | 1 | REPEATED ABSORPTION TIME
27 | 7.0 | 7.0 | REPEATED ABSORPTION TIME INTERVAL
28 | 5.0 | 5.0 | LOW TEMPERATURE LEVEL
29 | 70.0 | 70.0 | LOW TEMPERATURE CHARGE CURRENT
30 | ON | ON | WATCH
31 | Y | Y | BMS PRESENT
33 | 12 | 12.0 | POWER SUPPLY VOLTAGE
34 | 10.5 | 10.5 | INPUT CURRENT LIMIT
49 | 5 | 5 | BACKLIGHT INTENSITY
50 | AUTO | AUTO | BACKLIGHT ALWAYS ON
51 | 3 | 3 | SCROLL SPEED
52 | ON | ON | Buzzer
59 | 41 | 42 | CAN ADDRESS
60 | 0 | 0 | CAN DEVICE INSTANCE
61 | 1.11 | 1.11 | SOFTWARE VERSION
62 | NO | NO | RESTORE DEFAULTS
64 | NO | NO | LOCK SETUP
67 | CELC | CELC | TEMPERATURE UNIT