I want to install a multiplus 2 5000Va with pylontech us 5000.
But hhe isseu i have is that the inverter the costumer has is a single phase 6000Va this exceeds the 5000Va on the multiplus.
It’s a 3 phase grid is it ok that i put the multiplus on another phase than the excisting inverter?
Hi Nick,
If your customer has < 5000W of solar connected to the inverter, or you can program a fixed limit of 5kW in the PV inverter, then you are ok on the same phase.
Otherwise installation on a different phase, or with the PV inverter on the AC in side of the Multiplus, is ok too.
Also, please make sure that your battery can deliver sufficient current for the multiplus. A single US5000 battery is limited to 50 Amps continuous, this is insufficient for a 5kVA inverter.
Thanks for the reply.
2 pylontech us 5000 wil come.
Is it possible to only connect the ac in?
The multiplus only needs to charge and discharge the battery when there is to many or to low solar power.
Client doesnt need any back up function
Yeah it would be an ess for the beginning i would be only for the surplus for maximum self consumption maybe later for dynamic ess.
2 x us5000 would be the setup.
Do you recommed the us5000 in parallel?
Or the batterys connected with single pair of cables to the multiplus?
For the 5000W inverter, you do need 4 or 5 US500c as minimum, Due to the battery discharge limits.
Yes, it is possible to only connect AC in, I have a 3000W inverter connected like this.