Multiplus 2-3000 parallel with 5000 watt pv inverter

I currently have a situation where a 1 phase Growatt 5000 watt pv inverter is delivering power to the 1 phase grid.

I want to add 2 multiplus 2 3000 inverters in parallel between the 1 phase grid and the pv inverter.

Is it allowed to connect the no break outputs of the multiplus inverters to the Growatt inverter so each multiplus receives 2500 watt?

No way - one MP 3000 fails and Grid fails - Rule 1:1 - potentially very long black out…
Use a 5000VA and Growatt are happy talking to each other and you are within rule 1:1

1 Like

And when using the non critical load ac out 2 output, would that be allowed instead?

The reason I want to use 2 multiplus inverters is to be prepared for a 3 phase grid in the future, only having to add 1 multiplus (and of course replace the 5kw Growatt for 2 or 3 smaller ones or a 3 phase type)

Power produced has to be consumed or stored otherwise your voltage rises skyhigh amongst others.
Unmatched sytems introduce a risk.
In your case put a MP2 /3000´s in parallel with an external CT (max perm load 2400W @ 25C) Victron is rated in VA not in Watt (power factor) Thus you can have critical load AC1 and it can acount for overall PV production (ESS)
If it would be me I would simply put in a 5000. If later I get three phase and maybe EV just put in 2 more 5000 thats it, no need to split off the PV.
https://www.victronenergy.com/media/pg/MultiPlus_12V_500-1200VA_120Vac/en/installation/optional-connections/parallel-connection.html

1 Like

Thank you. Because of the information you gave me, I won’t connect the Growatt behind the multiplus but in front of it on ac in. When the grid disappears the Growatt will stop but that’s the trade off.

I also wonder what a reasonable power factor is to be expected, because at power factor 1, it can deliver 3000W I think.