This solution is mainly targeting Cerbo GX users that wants to extend Digital Inputs and Relays on their system.
Please note that there is a conflict with Kwindrem’s RpiGpioSetup that is targeting Raspberry pi users, but we have some users that reports to have successful setup with rPI and RemoteGPIO.
In order to have a reliable direct attached interface to the relay, I selected a Modbus/RTU based relay from Dingtian (also TCP, MQTT,… capable) that attaches on the USB port of the Cerbo GX.
There are many solutions for attaching relays via Ethernet, but I didn’t want the relays to rely on an external Ethernet network switch. That said, the driver is now also supporting this Dingtian device via Modbus/TCP.
This Dingtian box provide 8x relays, that can be controlled with Modbus Serial, but also over IP and with various additional protocols: https://fr.aliexpress.com/item/4000999069820.html
They have variants of 4 or 8 relays.
A USB to RS 485 adapter will be required, and I strongly recommend to go with a RS485 to USB adapter based on FTDI chipset, in particular FT232R and follow the instructions on how to program it.
You can find an extensive questions and answers as well as all the required links (As a new user on the new Community page, I’m limited to 2x links and 5 pictures in this post…) on the previous Victron community thread dedicated to RemoteGPIO here: RemoteGPIO (ex venus_rgpio) now released in v3.2.1 - VictronEnergy
Below I’m trying to capture most of the relevant information.
RemoteGPIO (ex venus_rgpio) now released in v3.4.2
Adding PARTIAL support for VenusOS v3.60 (The Digital Inputs are currently broken with VenusOS v3.60)
It is still requiring to run the Legacy GUI.
But with v3.60 the hope is big to get the native GUI V2 support with the control of the relays. I’m after it…
******* UPDATE Version 3.3.0 ****************
No more reboot required after configuration change, just ise restart RemoteGPIO services.
CPU resources optimisations: Overall cpu usage can be reduced by up to 75% depending on number of modules and options selected.
Several settings menu enhancements. Added option to enable/disable digital inputs per module. Added option to ‘Restart RemoteGPIO’ from the menu.
Thanks to Derrick (drtinaz)
******* UPDATE Version 3.2.2 ****************
Relays confirm to work with RaspBerry, but Digital Input won’t. It will require additional work for making Digital Inputs working with RaspBerry.
******* UPDATE Version 3.2.1 ****************
Removed option for 16x relay module. It will require different driver version
Added support for reading relays status and updating GUI. This option is set to default off in RemoteGPIO settings.
****** UPDATE Version 3.2 **********
Support for 2, 4, 8, and 16x relais modules.
Support up to 3x units.
Thanks to Derrick for adding the above
As we don’t have all the units here to test, thanks in advance to report here your experience with the 16x relai version.
****** UPDATE Version 3.0 ************
I am happy to announce here that version 3.0 is finally released with many changes.
Configuration is done from the Venus OS graphical interface, no more file editing is required.
The big change is how RemoteGPIO is integrated into Venus OS: it is now natively integrated at the D-Bus level, allowing the use of relays and GUI digital inputs straight from the GUI.
RemoteGPIO runs as a service in VenuOS without the need to run NodeRed with Venus OS Large. NodeRed is still supported for advanced integration.
I encourage you to upgrade to version 3.0.
As of today up to 18 additional relays and digital inputs are supported with two 8x relay Dingtian units. Both TCP and RS485 models are supported. I will add support for different Dingtian size models soon.
The latest GuiMods version must be installed. A big THANK YOU to Kevin Windrem for updating GuiMods and PackageManager in order to cooperate nicely with RemoteGPIO.
Thanks to the contribution from Thomas, RemoteGPIO is now version independent, starting with Venus OS 2.92 or later required.
For the boating community, I have some cool stuff coming up on top of RemoteGPIO, which I’ll be launching soon!
Specific setup for USB-RS485 adapters to work sine with no conflicts with other adapters such the ones used for various BMS:
I propose here a solution to better handle USB to RS485 interface with RemoteGPIO, making sure there will be no more conflicts with other services requiring the same model of USB to RS485 adapter.
The solution I Propose is to purchase an adapter based on FTDI chipset, in particular FT232R based. These are still inexpensive and have the advantage to be reprogrammed on demand.
Follow this procedure:
1/ Download FT_Prog - EEPROM Programming Utility from their website in the utilities page Utilities - FTDI
As of 7th March the version is 3.12.46.653
and install it on Windows (I tried Windows 7 successfully)
2/ Connect the USB to RS485 you wish to reprogram and select the driver you just downloaded
3/ Let Windows to search on internet the right driver
4/ Run FT_Prog
5/ Press F5 to scan the USB bus (go to menu DEVICES and select Scan and Parse
It should display a device in the Device Tree
6/ Select USB String Descriptors in the Device Tree and update the Product Description with « RemoteGPIO » (original value is « FT232R USB UART »
7/ Select Program in DEVICES menu
Hit Program button
8/ Hit F5 to scan again and confirm RemoteGPIO is now the correct Product Description in the USB String Descriptors
Note:
Note: The previous version is still available, you just need to change the branch (or tag) to “old” in PackageManager. The latest version is v2.4.2 and supports Venus OS from v2.92 to v3.22.
I’m glad to announce that finally I made available the USB Relay Gateway compatible with SetupHelper Package Manager.
All Venus releases from v2.92 up to currently latest v3.12 are supported and tested. And thanks to SetupHelper it will be fairly easy to maintain and support next Venus releases.
This package is mainly targeting Cerbo GX users that wants to extend Digital Inputs and Relays on their system.
In order to have a reliable direct attached interface to the relay, I selected a Modbus/RTU based relai from Dingtian that attaches on the USB port of the Cerbo GX.
There are many solutions for attaching relays via Ethernet, but I didn’t the relays to rely on an external Ethernet network switch.
A USB to RS 485 adapter will be required.
I selected this one as this is coming with a USB cable and can fit nicely on the Cerbo GX:
https://fr.aliexpress.com/item/1005004778767986.html
The RS485 must be connected on the first USB port of the Cerbo GX
SETUP:
The setup is now fully automated, no more requirement to issue shell commands! :slight_smile:
It runs only with VenusOS Large with minimum version 2.92
1/ Configure the Relay Module
The Dingtian IOT Relay module needs to be configured so Modbus RTU works:
Connect the ethernet interface of the module and access to its configuration page (192.168.1.100 and admin/admin by default).
Configure the RS485 with Protocol Modbus-RTU and set address to 1 (for the first unit).
For TCP control, configure the TCP Server with ModBus-RTU over TCP
Example configuration for 1st Dingtian unit
Example configuration for 2nd Dingtian Unit. Addr in RS485 needs to be set regardless control is RS485 or TCP
2/ VenusOS Large
Install the desired VenusOS Large version (minimum v2.92)
Optional: Enable Node-RED (Settings/Venus OS Large features)
3/ Install RemoteGPIO
Make sure SetupHelper from Kwindrem is installed. If not follow instructions from kwindrem Github SetupHelper project
Add RemoteGPIO repo if not already listed in the inactive packages RemoteGPIO Lucifer06:main
Download and install the package
BE PATIENT during the Installation of the package, it can takes few minutes as it downloads few Node-RED palettes
Reboot will be required for the USB to be not anymore preempted by VenusOS services
Using RemoteGPIO:
1/ RemoteGPIO can be used from VenusOS GUI to control 4x additional relays.
It is required to install Kwindrem’s GuiMods package (GitHub - kwindrem/GuiMods: VenusOS GUI enhancements and modifications)
Go to Settings/Relay there are 4x additional relays to be enabled and then use the dedicated Relay page that should display the additional relays
2/ RemoteGPIO can also be used with Node-RED
With Node-Red it is possible to use all 8x relays as well as the 8x digital inputs
During the installation of the package, the following Node-RED palettes are automatically installed:
— node-red-dashboard
— node-red-contrib-buffer-parser
— node-red-contrib-debounce
If there was no flows yet running the RemoteGPIO flow got installed
If a flow was already installed, in order to not break anything RemoteGPIO will need to be manually imported from the local library (Menu Import / Local / RemoteGPIO.json)
The RemoteGPIO flow is also adding a Node-RED dashboard for controlling the Relays and monitoring the Digital Inputs
RemoteGPIO v2.x is backward compatible with previous venus_rgpio
(Solution: Adding external Relays to Cerbo GX using one USB port - VictronEnergy)
Troubleshooting:
Any questions or suggestions about RemoteGPIO are welcome here
Most of the issues are coming from USBtoRS485 adapter been trapped by the wrong VenusOS service.
In order to make it working with default configuration file, it is important to attach it to the first USB port.
IMPORTANT If a different adpater is used, or if a different USB port is used (or connected behind a USB hub) the file /etc/udev/rules.d/serial-starter.rules will required to be tweaked accordingly so the USB-RS485 adpater is always accesible with /dev/ttyUSB0
Toubleshooting from command line with dbus
List of all dbus relays and their status:
dbus -y com.victronenergy.system /Relay GetValue
Close Relay 3:
dbus -y com.victronenergy.system /Relay/3/State SetValue %1
Toubleshooting from command line with modbus
Read Digital Inputs:
/data/rgpio/modpoll/arm-linux-gnueabihf/modpoll -m rtu -b 115200 -p none -d 8 -r 11 -s 1 -c 1 /dev/ttyUSB0
Close Relay 1:
/data/rgpio/modpoll/arm-linux-gnueabihf/modpoll -m rtu -b 115200 -p none -d 8 -1 -r 3 -s 1 -c 1 /dev/ttyUSB0 257
Open Relay 1:
/data/rgpio/modpoll/arm-linux-gnueabihf/modpoll -m rtu -b 115200 -p none -d 8 -1 -r 3 -s 1 -c 1 /dev/ttyUSB0 256
Check that no process are talking to USB0:
ps | grep USB0
Should return only rgpio services. If not, it may be required to reboot VenusOS for the serial-starter.rules to apply
Prevent USB0 to be used by another service:
/opt/victronenergy/serial-starter/stop-tty.sh ttyUSB0
I hope to able soon to update this post with all the correct links and pictures so you don’t have to go back to the Archive Community Victron page.
Thanks for your great mod! I just hope that victron will make it possible to port that mod to v3.50 (Gui v2)!
Hi!
Thanks for making this manual!
I have now just got the 8CH board and USB RS485 converter from the links above.
I have tried to program the USB/RS485 FT232R converter. When I search for it in FT_prog it says no devices.
I have tried two computers Win 11 and Win10, added the driver manually from FTDI, added the ftd2xx.dll into the installation folder. It will not detect the converter.
I downloaded the help files from dingtian and have tested the UartAssist program. There is a very small led that lights up when I send a command, so I don`t think it is dead.
When I insert it into the USB port of the computer, there is a larger led that lights up one time for approx 500ms.
Any tips would be very helpful!
I ended up with MQTT… Works very well in Node Red.
Hi there, just curious about your solution.
Does this still show the Relays on the Venus OS and are you able to control them manually from a Cerbo touch screen?
Or is all of this just automated via Node Red?
TIA
This will only show in Node Red. Not in Venus OS
My very first integration as using Node-Red.
I came up with current driver so both the relays and Digital Inputs are available like Cerbo internal ones.
I would like to explore MQTT as native driver to see if this is less CPU hungry. than current Modbus control.
There is a Dingtian box variant that seems to have RS 485 support.
“8CH ETH WIFI RS485”
https://www.aliexpress.us/item/2255800812755068.html?gatewayAdapt=fra2usa4itemAdapt
Would this work direct without the adapter?
Sorry for the late reply, somehow I’m not getting notifications on this thread…
I see that you ended up with MQTT, nice.
But the primary goal of this mod was to not rely on any ethernet network between the Cerbo and the Relai box.
Hence the USB-> RS485 adapter. The milestone to reprogram it is not mandatory but make it easier for the soup (you then don’t need to edit the /etc/udev/rules.d/serial-starter.rule
I encourage you to review the details on how to do it from the archived page:
https://communityarchive.victronenergy.com/questions/245584/remotegpio-ex-venus-rgpio-now-available-with-setup.html
This is the exact model we are using. But you need this RS485 adapter to connect to the USB port of the Cerbo
I have managed to upload all the pictures of the original post.
That said, it is worth looking at all the questions and answers in this thread, as there is a lot to learn from:
Is there still a requirement to use GuiMods to see and control additional relays? Put another way, if I just want to use two or four relays on my 4 port Dianting relay boards, can I control them from the stock v2 gui without loading GuiMods? Thanks!
Edit: I forgot to mention I am running VenusOS 3.60~25
Only GUI v1 with GUIMod can display a Relay control page with the additional relays.
We are currently stuck with GUI v2. I had hopes that Victron makes the relay page (access from top left corner) a bit dynamic, displaying current resources, but no :frowning:
So with 3.50+ you need to keep GUI v1 as default one.
Hi, I am struggeling with the f… USB-Interface. I bought a FTDI-Interface but it is not willing to keep the Data in the EEprom, no idea why. so I decided to buy the linked Cable-Converter and got a CH340-Chip-Version.
the first USB is the most left, I suppose. I do not understand what and how I need to tweak the Serial-starter.rules… and what function does the USB0/1/2 selector in the unit-1 configuration have?
any help/idea?
Stefan
Erläuterungsauflistung.pdf (5,9 MB)
Hello fguiot,
I read your article about RemoteGPIO with the Dingtian relay box with great enthusiasm and I’m currently trying to follow it step by step to set it up on my Cerbo GX.
I’m an absolute beginner when it comes to Linux and related topics, but I’ve still managed to get some parts working. Unfortunately, I can’t establish a connection between the Cerbo and the relay board via the USB/RS485 adapter.
I’ve tried running some Linux commands as described in the forum, but the results don’t mean much to me.
Would you be so kind as to take a look and maybe give me a tip on how I could solve the issue?
Many thanks in advance!
Best regards,
Michl
Hello Stefan, with CH340 based USB adapter there is a conflict (hence the reason I’m strongly advising to with FTDI and reprogram it so it doesn’t conflict). To solve your issue, you need to
1/ plug the adapter in the first USB port, the one close to the outside of the Cerbo.
2/ edit the file /etc/udev/rules.d/serial-starter.rules and make the following changes:
normally on line 8 you have;
#ACTION==“add”, ENV{ID_BUS}==“usb”, ENV{ID_PATH_TAG}==“platform-1c14400_usb-usb-0_1_1_0”, ENV{VE_SERVICE}=“ignore”
uncomment by removing the #
4/ Save and reboot. You should now have access to the Relays and play with the linux commands to confirm it.
Hi Fugiot, thanks. it works. Meanwhile I bought an additional FTDI-based. This one was programmable :sweat_smile: and the relays are acting much faster (not as fast as the internals) and more reliable than with the CH340-based adapter. so I am happy :blush:
Hi Michl,
I am not the best here, but… did you connect the groud wire (black) from the RS-485-Converter? I see only A and B on the picture. the black must go to the Ground (Minus)
This might be slightly off the initial subject but I was thinking in terms of a more direct approach using hardware and Node-Red if the relays are to be situated in the vicinity of the Cerbo unit.
BTW, I finally got my MQTT to work over LAN for a remote set of relays controlling my hot water tank.
However I stared to play with Arduino NANO (small and practical) with Node-Red’s serial out and initially got it to work, all I needed was to add some mosfetts to sufficiently amplify the signal in order to drive the relay coils.
However, strangely enough, when I came back to complete the job, Arduino would non longer respond to commands even though it shows connected to the node :thinking:
Any Arduino would be capable to drive up to 12 relays with the only disadvantage of not showing them on the display, but I guess that could be achieved using Node Red Dashboard.
I was wondering if anybody else had some experience with this :thinking:
Here is the MQTT controlled relay for the water immersion heater