Realtionship between current and load in VRM advanced charts

Hi - I’m clearly missing something but I cannot understand the relationship between the current and load in the VRM charts. The current seems to be excessively high (e.g. in the screenshot a load of 6kW is showing a current over 100A).
Appreciate some help understanding this.
Colin

System (A) is DC current so 6kW at nominally 50V is 120A?

Thank you - so that’s where I was going wrong - I’m calculating 6kW at 240VAC to be 25A but hadn’t twigged that VRM chart Current is being displayed at the battery DC nominal voltage of 50V!
… Colin

Well it will be at whatever voltage your batteries are at, not exactly 50V.

1 Like