Hi
I have 6 Quattro 15000 in a three phase system. Due to battery power I want to limit DC power what I can pull to 170A.
How can I do that?
Thank you
You have to set an inverter limit for that, in ESS options.
That is a very small limit for a large system. If you have a small pack, be aware you are likely to have issues for large transient loads or grid loss.
You can’t directly limit battery discharge, only the inverter limit, which is ignored at loss of grid.
1 Like
Hi Nick
You mean the option “Limit Inverter Power”?
I just dont want 6 times 200A - I rahter prefer to have 6 times 170A
In case of grid failure what is higly possible it is anyway not a biggi as I detect that with Loxone. In such case I cut of automatically several consumer.
Yip, you will need to set the limit in ess which will push more to grid and indirectly reduce the DC load.