Hi all,
I’m seeing odd SOC reporting from my Pytes V5 bank and would like to know if others see the same, and whether a firmware update fixes it.
System
- EasySolar-II GX + MultiPlus-II 48/3000 in parallel (VE.Bus fw 556), Venus OS v3.80
- ESS, DVCC on, Pytes on CAN-bus (can-bus-bms)
- 2× Pytes V5 (200 Ah total), battery fw shown on the GX as v24.1 (= 1.10.24)
- SOH reported 100%, cells balanced (~40 mV spread even at the bottom)
What happens
On discharge the SOC freezes at 20% until the lowest cell drops to ~3.17 V. On charge it freezes at 90% until the cells reach ~3.45 V, then jumps to 93%. A normal 1% step is ~2 Ah; these holds are 10–15× that. Data from VRM (1-min log), 18–25 Sep:
| Date / time | SOC | Held for | Ah while held | Cells (min/max) at start → release |
|---|---|---|---|---|
| 18.09 04:00 | 20% (dis) | 89 min | 19.5 Ah out | 3.21/3.22 → 3.17/3.18 V |
| 20.09 03:08 | 20% (dis) | 81 min | 20.5 Ah out | 3.20/3.22 → 3.17/3.17 V |
| 21.09 05:19 | 20% (dis) | 98 min | 21.0 Ah out | 3.21/3.22 → 3.17/3.18 V |
| 25.09 02:33 | 20% (dis) | 74 min | 19.8 Ah out | 3.22/3.23 → 3.17/3.18 V |
| 19.09 12:10 | 90% (chg) | 29 min | 31.5 Ah in | 3.39/3.40 → 3.45/3.47 V, then 93% |
| 20.09 12:03 | 90% (chg) | 24 min | 31.2 Ah in | 3.38/3.40 → 3.45/3.47 V, then 93% |
| 24.09 14:33 | 90% (chg) | 65 min | 30.3 Ah in | 3.36/3.37 → 3.44/3.45 V, then 93% |
Discharge current during the holds was ~15–19 A (~0.1C), charge current 50–70 A.
Capacity itself looks fine. From 100% (cells at 3.54 V) down to the ESS minimum (“15%”) the bank delivered 182 Ah / 9.5 kWh (19→20 Sep) and 180 Ah / 9.4 kWh (20→21 Sep).
The practical problem is the bottom end. At “15%” the cells rest at 3.18–3.19 V. This morning the grid disconnected while the SOC was at “15%”. The MultiPlus drew only ~5 Ah (~18 A for 17 min) before it shut down on low battery at 49.0 V (cells 3.04–3.08 V under load). During those 5 Ah the SOC dropped 15% → 3%. So the ESS “15%” reserve was really only a few percent.
Also, on days without a full charge the 20% hold doesn’t appear and the SOC drops quickly instead. Between “21%” and “15%” I measured anywhere from 4 Ah to 32 Ah depending on the day. That makes the ESS minimum SOC an unreliable reserve.
Questions
- Is this the expected behaviour of the Pytes BMS (voltage-anchored SOC correction at 20% / 90%)?
- Has anyone seen this improve with newer V5 firmware (1.10.27 / 1.10.29)?
- Until then, what min SOC would you recommend with this BMS, so the ESS reserve is actually there when the grid drops?
Thanks!