Pylontech showing 100% but voltage only 49.8V

Good day. I have 2 pylontech up5000’s connected to a 5kva Multiplus II with a MPPT charger.
Keep getting a low battery voltage warning. System shows 100% SOC but the voltage varies from 49V to 50V. Tried reseting system (including batteries). Latest firmware installed. System was working fine for a year. Any ideas on how to get the voltage and SOC to sync?

Please add some screenshots from the VRM Dashboard and device list.


Busy trying to discharge the battery to 20% and recharge again.

What are the min and max cell voltages?
You might have to make it sit on keep batteries charged.

1 Like

49.8V is normal when the Pylontechs are starting to discharge, even at 99%. See my graph below.
Question is which is the voltage when the battery current is 0A, at 100%, when the battery is idle. Mine, see, it’s 52.5V.
Also, see what’s in the configuration at: Settings - DVCC - Controlling BMS. It’s Pylontech?

Hi Alex. Seems to be a issue with the slave battery. Once I disconnect it. All the value started making sense again. Have sent the battery in to get checked. Thanks for the feedback

1 Like

This is an interesting chart. The Pylontech US5000 manual says the battery will shut off at 44.5V which is much less than what your image shows (if I’m reading it correctly it shows an empty battery at 48V).

Those ranges on the graph are set manually in such way that they are easy to read comfortably.
There is no correspondence/sync between the ranges and/or parameters.
The 48V<->53V range window is just taking the same space on the graph as the 0<->100% SOC, the same as the 0<->150A range or -70A<->70A range.