PV dynamic power limit 0W Venus OS v3.60

Hi all,

Since Venus OS v3.60 I’m able to control my Enphase system with (D)ESS. I’m using DESS so when energy prices are negative it would stop the Enphase system producing solar energy. I’ve tested that it actually works by switching off DESS and by turning off grid feed-in in the ESS settings. I saw the Enphase system throttling to 0W grid meter, so that works beautifully.

The next day I saw that the PV system wasn’t producing. I checked the PV system in the remote console and saw that the ‘dynamic power limit’ was set to 0W, which it was before 11kW. After restarting the Cerbo the limit jumped back to 11kW and the Enphase PV system started producing again. Now every day this is happening and I need to restart the Cerbo to reset this PV power limit.

What could be the issue here? Is this a bug? The energy prices are positive so it should not effect the PV power limit. Another questions; why is the PV power limit set to 11kW? My Enphase PV system is able to produce more than 11kW.

Hope you guys can help me out :slight_smile:

Anyone with the same problem?

Hi @darryl12123 , I see the same behaviour in my system.

Hi all,

Could you guys do me a favour please. When this happens again, instead of rebooting, disable the limiter function in the PV-inverter menu, and re-enable it again after 5 seconds or so.

This will give me an important data point.

The problem could be that a power limit of 1.5% is too low for Enphase to start up. Specifically, the limiter code will set all inactive inverters (those that don’t report a running state, and is making no power) to a limit of 1.5%. It is known that some Fronius inverters won’t start up under 1%. Maybe Enphase has a similar limit.

Hi Izak,

Sure I’ll try that.

Hi Izak,

So I switched on Dynamic limiter and straight away the Enphase PV system goes to 0W, see below screenshot:

I tried to switch off again the dynamic limiter and switch it back on after 5 seconds, but the dynamic limiter stays on 0W. I did not restart the Cerbo.

It is here now midday, 12:37PM and sun is shining and energy prices are possitive, not negative, so PV system should produce and sell back to the grid.

Thank you @darryl12123 .

I traced the problem to what I think is an incorrect implementation of the DER Capacity information model (model 702) by Enphase. I have yet to confirm, but it seems the WMaxRtg value (maximum power the device is capable) is not a static value, and sometimes it advertises zero as its maximum power rating.

If you reboot the GX device at such a time, or if the network connection is lost and a reconnection is made, it will think the device has a 0W maximum power, and 100% of zero is of course still zero, which is why it gets stuck there.

So short answer: Problem in the Enphase firmware. At least, it looks to be that way. I’ll have to wait until after dark (in the Northern hemisphere) to confirm.

Thanks for figuring this out. Please let me know what you find the evening.

Do you make, on behalf of Victron, a report to Enphase that their firmware has a bug (if it is their fault)? Or do we need to report it ourselves?

Also, do you know why the update interval changes when switching on dynamic limiter? With the limiter off the Enphase values are updated every second, but with the limiter on it only changes every 10 seconds or so.

OK, confirmed. At night, the Envoy publishes a maximum power rating of 0W. My guess would be that it publishes the sum of the online units, and when there is no sun, they are all sleeping.

Sunspec requires this value to be static, and not dynamic. So this is an incorrect implementation by Enphase.

I have a colleague who is in contact with them. I’ll see what can be done through that avenue first.

Hi Izak, thanks for figuring this out. Missed your request yesterday, but it seems @darryl12123 did not :grinning_face:. Thanks!
I can confirm I have seen the 0 W limit as well.
Also, this problem did not occur in the previous Enphase firmware.

That sounds great. Please keep us posted :grin:

Now I have the same problem with the 0W power limit. Is there somewhere a documentation how the dynamic power limit exactly work?

Does this change the power export limit (PEL) or the maximum power production of the Enphase system?

Here olso every morning I have the same problem with the 0W power limit. Is there solution for this problem please help!

One workaround could be to set a grid profile in Enphase that is limiting the export and not limiting the export in Venus OS. Enphase is currently working on a fix on this, but that could take another few months…

For this you need both production and consumptions CT’s installed on the Enphase Envoy to be able to limit export.

My thanks Manuel and Darrel for your response and input.
Darrel, what do you mean by “both production and consumption CTs must be installed on the Enphase Envoy to be able to limit export?” I have a single-phase with both production and consumption connected to my Enphase Envoy.
However, know I followed Mr. Izak Borger’s advice: every morning the limiter function must be manually disabled in the PV inverter menu and re-enabled after 5 seconds. and then start Enphase system immediately with producing again, until the end of the day, the next morning, doesn’t start again, and I have to disable the limiter function in the PV inverter menu and re-enable it after 5 seconds again !!!.

Hi. I believe I’m having the same problem. In my case, when I enable the function to limit the photovoltaic production of the microinverters to 1000W (for testing), the production always drops to around ≈10W. For some reason, after a few minutes, it sometimes begins to regulate correctly, bringing the microinverter’s photovoltaic production back to around ≈1000W. When this happens, the limitation holds until the next day, but the following day, the production is again at about ≈10W. If I try to enable and disable the function several times, I can sometimes get the limitation to work correctly (without having to restart the Cerbo GX), but always afer about 10 minutes have passed since its activation and after the photovoltaic production has previously dropped to ≈10W. When the function is working properly, I’ve been able to see the PV SETPOINT value change on the Enphase page “Enphase Energy - Enlighten | Sign in to Enlighten, but it seems this value only updates every 15 minutes, and I haven’t been able to see this value anywhere else in the system. The version of Cerbo GX is: 3.66 and Envoy: D8.3.5167.250527

Update: It is possible to see the PV SETPOINT value with
Endpoint: /ivp/sc/status
Method: GET

Hi Isak,

interested to know the outcome here as we are all impacted by this wrong behavior from Enphase<=>Victron interoperability

Hi Izak,

Do you have an update regarding the wrong implementation on the Enphase side? I just tried again to switch on Dynamic Power Limiter and production went straight away to 0W. After restarting the Cerbo it started to to regulate. Weirdly it is not giving full PV production. My batteries are 100% full, energy prices are postive and DESS in trade mode. Dynamic Power Limiter jumping between 3500W and 6000W (PV system could produce at this time 10kW). I don’t know why the limiter is this low and why is it fluctuating that much?

Nevermind to the above, I had the feed-in power limited to 1000W. Now removed the feed-in power limit and Dynamic Power Limiter is now at 11kW steady. I’ll leave it for now on and I’ll see if production starts up tomorrow.