Problem 2 X Multiplus II on 3F grid
Next problem with 2 X Multiplus II on a 3F net.
1 X multi-plus on L1
1 X multiplus on L2
1 x Cerbo GX
1 X EM24 ethernet on mains
1 X EM24 ethernet PV measurement
4 X Pylontech US5000
System configured as dual phase 120
AC out not used
When switched on, everything seems normal, but after a while the 2 inverters start to compensate each other. For example -3000W on L1 and +3000W on L2
Total grid power remains approximately 0
Does anyone know this problem and solution?
Thank you!
Is the ESS assistant installed on both MultiPlus correctly?
Thank you for your quick reply.
ESS is only installed on L1, I thought it wasn’t necessary on L2?
Read the manual:
https://www.victronenergy.com/media/pg/Energy_Storage_System/en/index-en.html
Problem solved!
Thank you very much!!