Power-in and distributor fuse for the Multiplus II 6k5
I’m a new victron user about to embark on my first ess build.
I’ve (pre)ordered 3x Multiplus II 6k5 and am designing the rest of the system now, current topic fusing.
I see the regular multiplus ii have a chapter called “4.3 connection of battery cables” which includes some cable/fuse guidance.
Opening the same chapter in the Multiplus II 6k5 manual shows an empty table, probably because it’s still in the making.
Can anyone recommended the power-in and distributor fuse size for my system?
I have 3x Multi II 6k5 with 3x 16kWh/48v battery bank in parallel.
Thanks!
Which victron power in do you have? With the T Fuses? also which battery bank?
If max discharge rate of the BMS is 200a per battery i would recommend Littelfuse class-T 225A 125V
For the distributor side to the 6k5 i would go with mega fuse 225a
Thanks!, should have added those details
The power-in is the t-class and the cable length is 1m per cable (A total of 2x 2 meter positive and negative run between inverter and battery (times 3))
The batterybanks are 3x a Gobel Power GP-SR1-JK314 with 16x314Ah per battery. JK-BMS with a 200Amp breaker.
Max discharge is 200a. So tfuse 225a is okay for the Battery’s.
On the distributor side. You can properly go a little bit higher on the fuse side of the mega fuses to 250a. For the 6k5 it is 11kw max output. 11kw / 48v = aprox 230amp
If you take a look at the victron docs for the old multiplus 48/8000. they advice a 300amp fuse.
Megafuse is marginal for 48V lfp, AIC of a potato, perhaps some NH type fuses for each inverter that can actually handle the available fault current from the lfp batteries?
@zyx360
if you haven’t ordered the Lynx yet, I recommend:
2x Lynx Distributor
6x 200A Adler EF3 fuses which fit into the MegaFuse holders
Adler EF3 can clear 50.000A instead of 2,000A of a MegaFuse.
For the Distributor, you can add a small I2C-USB adapter from AliExpress and flash an open-source software to get fuse monitoring including alerting in VRM and Venus OS.
If you aim for a main breaker between battery Lynx and MP2 Lynx, go for specialized Jean Mueller NH00 DC breaker which can handle 80V DC up to 800A.
If you ever find a source in the US for Adler EF3s please let me know. Ecs-online doesn’t ship out this way.
Maybe ask rayotech.de . They shipped to UK once.