Power Factor improvements

Good morning,

Recently we came across one single phase 8KVAR (6KW) Quattro inverter with a single phase 2.2KW water pump attached at 300 metres distance from the inverter.

The pump pulls nominal about 8-9.5A at 230V (pending pressure) but during start 38-40A, 4 times its nominal power and the inverter gives an overload warning very short.

After checking the power factor, we discovered it to be only cos phi 0.2 inductive, very low indeed due to the long cabling as well of course.

We will install a basic Power Factor control device instead of a soft starter or power factor controller as it only occurs with this pump.

The relay is for 3 Phase, but we will just connect the Neutral (1st main contact) and Phase (2nd main contact) to the inputs and the outputs to the capacitor, the 3th main contact (we take the resisters off) and the 4th main contact are used to switch the motor starter relay.

The little block on the relay is also a relay what closes about 5-10 milliseconds faster then the main relay below it, the wires you see are resistor wires and will pre charge the capacitor before the main relay closes and so preventing big currents and sparks.

When the main relay closes the capacitor is charged and now the motor will start with power factor cos phi 0.9-1 inductive, now the motor will only pull about 2-2.5 times its nominal current and starts due to that very fast without the inverter giving an overload warning.

After it is started the power factor will be about cos phi 0.85-0.95 capacitive, but that is also good.

With such a device, for about 50-75 euro the issue is solved, instead soft starters or power factor controllers which are quite expensive and must be programmed which is not for everybody.

Please let us know what your experiences are with power factor improvements

With the very best regards, Jeroen.

3 Likes

Good afternoon

The results are in.

During the time the solar is not active we activate this capacitor, then it pulls between 16 and 25A only, this due to resistance change at cold cabling during the night and “hot” cabling late afternoon as the ground heats up.

During that the micro grid is active we disconnect the capacitor system, this as the solar inverter corrects already the power factor itself, check your settings in yours…most can be programmed to cos phi 1.

So, results, no sun, 16-25A with capacitors instead of 38A, with sun and no capacitors with the inverters correcting pf cos phi to 1 20-25A, we call it succes, no more overloads.

How we did it, easy, just a with light sensor switch set very late, switching off the capacitor relay system only with a lot of sunlight.

I hope this can help many people who have simular issues with their hydrofoor pumps, specially off-grid systems.

Be aware, solar inverters connected to a micro grid with a lot of capacitive loads cannot correct this as all (most pro ones only) are made to cope with inductive loads which they can correct (only up to a point) when programmed properly, so, connecting capacitors during sun production is not an option and not adviced.

If any questions for your specific installation with similar issues, please let us know, and we will advice accordingly.

Regards, Jeroen.