OK, first, thanks very much for the help! I really thought that the Victron would just bump all the line voltages to a perfect 120v and boost as necessary, that’s on me.
I wanted to buy a Hughes Autoformer because I always felt that would fix everything. But…they aren’t made anymore and the used ones are basically $1000 still so, based on my previous (incorrect assumption) I figured I’d buck up another $600 and replace the inverter thinking it would do the same and I’d get pure sine wave and all the latest and greatest features.
With respect to testing the unit for the issue, I eliminated it some time ago. Going from memory, I upgraded the washer breaker to 20 amps and also replaced the receptacle with a 20amp unit. I then measured the voltage going into the transfer switch and after to check for drop. There was none. At one point I did clean the contactors in the transfer switch. I also polished the prongs with brasso on the cables. I have tightened all the connections in both the transfer switch and at the breaker panel inside. This was long ago and there were loose ones from the factory and from time to time I check them again.
I also replaced about $500 worth of parts in the washer thinking I had it beat. It was all unnecessary.
The conclusion I came down to was that the unit is tight and that the problem was park power. It is intermittent but it presents this way, the voltage will always be low. Turning everything off inside will help the chances of success. It happens more in the heat of the summer when park power draw is high OR when in a park with goofy power.
The park I’m in right now is brand new. Very few people - it’s almost deserted. With no loads the line voltage is 120V. Start turning on things like electric heater (1500 watts) and the line voltage starts to drop. The more you turn on, the more it drops. If I’m using the dryer at anything around 115v it could act up. Anything like 110v and it’s almost a certainty. The damn thing injects water during the dry cycle
My thinking was erroneous. It was autoformer or victron inverter. I thought the inverter did the same, and if anything, did way more.
I still don’t know what power assist even does. I can see it operate, it’s operating when the dryer is running, it just doesn’t seem to do anything. I’m wondering if the answer lies with Paul’s post above regarding UPS functionality. When inverting the unit puts out ~118v at the outlet.
This causes me to wonder, can I set the unit so that it goes to UPS mode at something like 115v? In other words, disconnect from shore power and go UPS? It may be that there is another way to skin the cat but I’m not sure. I thought power assist would fix this but I certainly understand that if it’s connected to shore power and shore power was 110V and it boosted to 120V it would try and raise the power in the park.
There is good news, the microwave seems to be much faster!