The Issue I have is:
I have a brand new Multiplus 24v 3kw unit that doesn’t correctly indicate the DC voltage on the battery terminals, and is a bit off on what it shows the input grid frequency is.
My background:
Retired now, but I spent over 34 years in the hydro power industry as an electronics / control system / communications tech, and was a foreman over the meter / protection shop, as well.
I have had training and experience in maintaining and repairing power control systems, and several older style ferro-resonant single phase and 3 phase UPS systems, as well as several PWM style units.
About the only background I have on these smaller units is from helping a friend when he had problems with a 8kw 48v Outback split phase unit in his off grid cabin. He had about 4kw of solar, a small Kubota 7.5 kw gen set, and it had some great big diesel locomotive starting batteries for about 60kWh of energy storage.
System:
My system is composed of a 100/30 MPPT controller, a Victron 500 amp Smart Shunt, and a 24/3000 Multiplus unit.
Energy storage is 400 Amp hours of 24v LiFePo made up of 4 strings of 2 each 100ah 12v batteries. All battery connections are made with #2 awg cable.
They are all fused at the individual battery string positive terminal(s) with marine style 100 amp fuses and each string goes through a 100 amp breaker to be paralleled up on a 400 amp junction block, which is further connected to a 350 amp positive distribution bus via 1/0 awg cable.
Negative #2 awg connections are all paralleled up on a 400 amp block, and the 500 amp smart shunt is connected to that junction block via 1/0 cable and on to the negative distribution block, also with 1/0 cable. The Multiplus is connected to the distribution buses by #1/0 awg cable, with a total run length, (negative + positive) of less than two feet of 1/0 awg.
In terms of performance, it works just as advertised, and quite well at that.
The Problem:
The issue is that the Multiplus is not displaying the DC voltage accurately, and it’s making fine tuning the DC absorption and float voltages a pain.
The Multiplus reads almost exactly 0.4 volts LOW. My Fluke 87 on the DC terminals will read 28.0 volts, the Multiplus reports 27.6 volts.
All of the other Victron Devices match within ± a digit or so of what the Fluke 87 indicates. (As did a 24/1200 Phoenix I had in this system for a short while.)
If the MPPT said the battery voltage was 27.23 volts, the shunt would indicate 27.22, the Phoenix would say 27.24 or in that ball park. The Fluke 87 would indicate 27.23, so basically, everybody agreed with each other.
Swap the Phoenix out for the Multiplus, and it indicates almost exactly 0.4 volts LOW.
Meter, shunt, MPPT all still agree with each other. Multiplus is the odd man out.
Well, no big deal, just apply an offset, you say?
The point is, I have checked THREE other Victron devices and they were ALL DEAD NUTS ON as compared to the Fluke 87. (Which, by the way, was checked several years ago against a NIST traceable calibrator…)
That does NOT sit well with me. Three other Victron devices are right, and this one isn’t??
Ok, fine, lets try the offset…
Ran into the NEXT issue.
When the unit is CHARGING, it OVERSHOOTS the set point that I’ve programmed in. Watching the voltage via a meter directly on the Multiplus terminals shows an excess of well over several tenths of a volt in excess of the setpoint. (The remote voltage sense wires are NOT connected, and it didn’t make any difference when I DID connect them.)
In other words, if I want absorption to sit at 28.1 volts, I’ll set the Multiplus to 0.4 less than that value, (IE: 27.7 volts,) and watch the meter on the DC terminals of the Multiplus shoot up over 28.4, 28.5, and as high as 28.6 volts, and it will HOLD that voltage. It doesn’t just overshoot and drop back, it stays there for a while, which is enough to trip off the ‘charge switch’ in some of the batteries internal BMS. When that happens, the other battery in the string no longer gets to sit and finish the top balance cycle, because there is no longer any current flowing in that string.
So, to keep the overshoot from triggering the BMS in the individual batteries, I have to offset the set point by the measured STATIC offset of 0.4 volts, PLUS the ‘overshoot’ value of almost 0.4 to 0.5 volts. That makes the set point in the Multiplus almost a full volt below where I want it.
One OTHER issue:
Also, the Multiplus indicates 60.3 Hz on the input, and 59.9 Hz on the output, and this is with the pass-through relay CLOSED.
Fluke meter says grid is bouncing around at about 60.02, 60.01 etc. Hundredths of a herz changing values is expected.
BTW, if we had a grid frequency of 60.3 hz, we’d have been scrambling to drop generation…
Anyway, the local Victron dealer wanted me to just swap my unit for one of theirs in stock. I said sure, but FIRST, you drag it out of the box, hook it up and see if it measures ‘off’ like mine does.
Yeppers. Right out of the box, it shows that with a voltage of say, 27.0 volts DC on the input, the Multiplus reports 26.6v.
Same thing with the input frequency. Shows 60.3 Hz. Output shows 59.9 Hz.
I HAVE updated the firmware in my Multiplus to the latest firmware, (according to Victron Connect,) so if it’s a problem with older firmware, well…
So, Victron, do you have an issue with calibration of this line of product, or?
Steve