Our home 3 phase ESS system in Bleiswijk (the netherlands)
Hi from bleiswijk the netherlands!
Sept 2025 *new updated system*
Our home self build 3 phase ESS system consists of the following components:
2 multiplus 2 3000 48V
1 multiplus 2 3000 48V GX
3 multiplus 2 5000
1 cerbo gx mk2
6 bluesolar mppt 150/35
4 pylontech US 5000 batteries
CG EM540 energy meter on main grid
CG ET340 for oven and ceramic cooking (AC in side)
CG ET112 and ET340 for heatpump (AC out side)
8 JA solar 345Wp panels
16 JA solar 415Wp panels
All of them in 2S2P per mppt
System is self installed (i’m an electronics engineer)
Its running flawlessly for almost 2 years now, our whole house is connected on the ac outputs.
from half februari till half november we use power almost only from batteries and solar
Very impressive system, I see you have built your own bus bar system rather than use a Victron Energy Lynx, how did you get on building your own bus bar and protection devices?
Thanx!
Yes i did, in the top small grey box are just switches to disconnect pv and there is a second small box with overvoltage/overcurrent protection units for every pv string (that box is not in the picture)
The middle one is the fuse box with midifuses and holders for the mppt in and ouputs these are then connected to the main busbar in the big grey box
In the big grey box are the main fuses, 3 for the multiplusses and 3 for the pylontechs and the busbar for the whole system
Also there are 3 switches to disconnect the batterys
Not in the picture: 2 emergency stop buttons to turn off the complete system including the batterys
One is in the ESS room (that room is only accesible from the outside) and one is in the main house distributor in the room next door
Nice system !
Like the Pylon masks… From where did you get them?
But… You didn’t followed the rules for cooling…
No offense, just saying… Many don’t follow this Victron recommendation.
For MPPTs, manual, page 10, 4.1. Mounting.
Observe a minimum clearance of 10cm under and above the solar charger for optimal cooling.
You know that they are using natural convection for cooling and the cooling element is on the back…
And considering that the MPPT itself has 13cm in height, you should have a gap of similar size between MPPTs and grey thingys.
Thanx!
Those are 19” 3HE security covers from adam hall
You are right with the mppt’s, however at max production in my system the only get about 35 degrees so not that warm
The multis was a space issue but i built in extra cooling at the bottom of the multis
and the room has extra ventilation, air is activly vented out from above and fresh air is coming from below (outside air)
I will take some pictures of the extra cooling!
I noticed this as well. A lot of DIY folks may find them too expensive, and there are other workable solutions.
I would recommend to lift the MPPT’s with “stokschroeven” :slight_smile: a few centimeters
Hoi, ja hoor dat kan, even kijken hoe we veilig gegevens kunnen delen, aangezien er geen prive bericht mogelijkheid is op dit forum
kan geen mail delen, bericht is gelijk verwijderd en met mijn account kon ik geen berichten meer zenden.
ik denk dat ik weet waar je woont, vind je het goed als ik eens langsfiets.
Hier mijn vrm link om alvast even te bekijken :blush:
Hey @DuivertNL, nice system! Out of curiosity. How accurate did the MPPT calculator on the Victron website predict your pv generation and how does it compare with your real world results?
How many months a year can you be ‘off grid’ without importing from the grid? Do you cook and heat your house on gas?
Thanks for sharing your system and info!
Hi i did not use the calculator, i choose one by myself but only on specs
So no prediction on pv production, because you can use a location but not angle and direction as far as i know in the calculator
Im not fully off grid, ESS always needs grid to balance, but on average i can use pv/battery from mid/end feb or begin march to avout begin/ half november
I have a gas connection but only partly for heating/shower, we also have solar water heating
And we use ac and also partly electric heating, cooking is also electric
We have a fairly large house (180m2) ,
average yearly gas usage in NL is 1500m3, ours is about 400m3
Average yearly kwh in NL is 3000kwh, ours is about 650kwh
We could get more kwh out of the system but i like to keep about 30-40% soc for grid failure
Our 9600Wp produces about 8500kwh yearly
That’s pretty impressive. I wouldn’t have thought you can run electric cooking plus the rest of the house on 3x3kVA MP2. Most people seem to run 3x5kVA or even 3x8kVA to maximise the 3x 25A house connection. I guess that depends also if you an electric car that needs charging.
Yes its possible because you can use multiphase regulation, however if i would install a new system or update the current i would go for 5000 multis
Take a look at this:
Hi Marc,
Elsewhere you write you have a custom emergency solution which, not only, shutdown the inverters but also the pylontech batteries.
Can you provide some more information about this solution? Especially the battery part.
I currently have a esp32 connected to the console of the master which can shutdown the batteries, but this solution does not seem too reliable.
Would be great to see some other solutions out there.
Thanks, Trant
Hi
The pylontechs have a contact connection (RJ45)
Pin 1 and 2 are for remote on/off, i use these with a relay for emergency shutdown
So i have a a 4p emergency switch with 3NC and one NO contact, the NC are for the multiplus remote on/off, they supply 12v to a relay (4 pole NO/NC) the contact on the relay are connected to the pylontechs remote contacts (4x US5000)
there is also a 4p manual reset switch so the pylontechs can start after an emergency shutdown and power the system on again
Great, I seen that some time ago but did not pursue that as I did not quite get how to use it.
so one of the multiplus remote on/off is powering another relais because 12v flows through the multiplus remote on/off?
If so that is clever.. I would need 6 to 8 battery relais, so I just use 2 times 4p on two multiplusses?
How did you do this?
Do you have some simple schema’s I could use? (Dutch is no problem).
Thanks, Trant
No the multis have a 12v output terminal, and one of them powers a small 4 pole NO/NC relay, so that relay is always powered in normal working state
each NC contact of the relay is connected to each battery remote contact
The emergency stop button has 3 NC contacts, each NC contact is connected to a multiplus remote contact, so when i press the emergency stop the multis shut down, the relay shuts off and makes the NC contacts, this shuts down the batterys
the reset switch has 4 NC contacts, these are in series with the relay to battery contacts so the batterys will start