Hi all,
It is not clear to me what this means. Are these parameter for the charger?
The minimum CoC is 30% why not 10% e.g.?
Actually in my Cerbo the min. SoC is set to 10%. This works quite well …
You might try to use ve-config in english ?
This is the value for “end of charge”, normally 100%.
Thank’s for feedback!
Who is charging? … charger of the MP2?
What happens when I deaktivate battery monitor?
You cannot use ESS assistant if you disable the internal monitor.
If your battery has SOC and you have a GX (if no an ess assistant) then you will be fine disabling that.
As an fyi that top number is usually 85% or above depending on your battery type as it refers to the bulk charge time the battery spends. So if your charge efficiency is 97% then bulk is also probably 97%.
Ok understand … battery monitor has to be enabled otherwise ESS does not work!
I also understand when I put 30% into that input charger only load to 30% SoC then bulk is finished. Means whe grid shut down only 30% of battery capacity are available for backup.
However this is ony true when ESS is NOT active. If active seems this has no meaning. E.g. I use 10% as min SoC in the ESS and the system doesn’t care if I put 30% or 90% into the battery monitor.
Thanks for help!
There is a manual here. It explains settings.