Multiplus split phase issue

Ok I think I understand now. My gen Runs to a sub panel. Then from the sub panel L1 hot neutral ground go to one multi then L2 hot neutral ground go to the second multi. Both neutral going out are connect to the bus bar in the sub panel and ground is wired the same to the bus bar in the sub panel. The double 30 amp breaker on the right goes to the multi IN and the 50 amp breaker on the left is where the gen comes into the sub panel. I have the AT wired the same as the diagram. I did not change any relays on the AT or the Multi. Also attached is the gen wire diagram.